What's better Burnham vs lochinvar
captin94
Member Posts: 4
in Gas Heating
Trying to choose one I'm looking at the Burnham ec3 I think and the lochinvar solution two stage boiler which is better and what would you choose? Thanks
0
Comments
-
Both are good boilers. Each has advantages and disadvantages. What kind of system (cast iron radiators, fin-tube baseboard, something else)? Has a heat loss calc been done?0
-
I used the Solution for a couple seasons and I really wanted to love it, but I couldn't. It's a great concept for a boiler, and my guys loved the weight of it, but it has some limitations that made it not ideal for many applications. It's also far from Lochinvar's favorite product. After the Solution experiment (for lack of a better word) I put more effort into explaining the benefits of true high-efficiency boilers. The Knight is a far superior product.
Think about that, why don'tcha?Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
I have base board heat need 79k btu from what I have found when calculating.0
-
Are those calculations from the building heat loss, or the EDR of the baseboard?--NBC0
-
I found the number by 119ft baseboard so I took 119x580=69020 btu so that why I'm looking at the 79k unit or is this to large.0
-
The amount of baseboard tells us the upper limit of boiler size, not the correct size. If that's Fine/Line 30 you're going to get more like 520 BTU/ft and you need to knock 6" off each convector if you measured the cases.
If your contractor installs a KHN-085, you don't need to bother with the heat loss calc thanks to its 10:1 turndown, one of the lowest minimum firing rates there it. If you're using a boiler with a lower turndown, someone needs to do a proper heat loss evaluation on the building.0 -
Ok thanks and back to main question which is better boiler for the buck / budge guy thanks0
-
Lochinvar KHN is an awesome boiler.Steve Minnich0
-
If you are asking about the two in your original post, the Burnham is a better choice for your application.
Three of us here would choose a KHN-085 for that job.0 -
Look at the Burnham K2FT this is their fire tube heat exchanger model.
For you to get the best bang for your money a condensing boiler needs to run at low water temps.
If you have copper baseboard there is not much water in the system and most likely the boiler will need to send out higher water temps to heat the house.
You can use the Burnham cast iron boiler and still do outdoor reset and not condense the boiler.
How are you going to vent the boiler?
Condensing boilers vent side wall or vertical with PVC pipe and fittings or other materials.
Cast iron boiler you can vent up a chimney with a aluminum or SS chimney liner.
W/M has their GV90+ cast iron boiler with external heat exchanger and it vents with PVC pipe and fittings.
Don't forget when buying expensive condensing boilers and the parts fail out of warranty some of these parts are very expensive.
Burnham and Lochinvar condensing boilers have 5 year parts warranty no labor coverage.
Do your home work just because a high efficiency boiler has a 95% AFUE connecting it to a system that requires high water temps to heat the home the efficiency can go from 95% AFUE to 86% - 89% AFUE.0 -
I believe the ec3 has built in boiler protection and will accept 110 degree return water. If you wanted cast iron and lower temps0
-
Compare the upfront cost vs possible savings. In cold weather, the mod con may be running 85% or so efficiency if it isn't condensing. Mild weather it might have return water cool enough to condense. So a home with baseboard won't see near the savings as a home with converted gravity huge radiators or radiant heat running 110°. Then factor in possible repairs as components in mod cons can get pretty salty and there's lots more to go wrong than with a mid efficiency cast iron boiler.
0 -
Wouldn't the modulation of the firing rate offer any savings compared to the mid efficiency boiler? What about the more even heat from longer run times at the lower rate? Wouldn't that be more comfortable than the on/off full input nature of the mid efficiency? I'm not sure what that would be worth compared to the added maintenance of a modconYou can have it good, fast or cheap. Pick two0
-
Our building has both a Lochinvar wall hung fire tube and the floor standing coil HX model. The new floor standing fire tubes with 10:1 turn downs are pretty cool. Our building's contractors replaced a cast iron boiler running through an ergomax reverse indirect water heater. Our radiant floors and DHW was heated by the ergomax. I came in right after they took out the cast iron and ergomax, which I believe would have been better to stay with. The only reason they upgraded was to make $$ and our management was dumb. The two Lochinvars were originally staged together and heated a loop with the loads piped into the loop with closely spaced tee's and more pumps. This arrangement added a bunch more pumps and caused the Lochinvars to short cycle like mofo's because there was maybe a couple gallons in the main loop. The Cadillac Lochinvars were running at 160F with tekmar mixing vavles everywhere. Complete disaster. We seperated the system and the Lochinvars have been running strong for 6 years with no maintenance, except for the condensate neutralization. Lochinvar states in their service manual you don't need to clean the coil HX until a certain delta in the water temp probes exists, which indicates carbon build up on the HX. I recommend the Lochinvars 100%. They were heavily abused for a year and are still going strong.
With that said, if was around earlier, I would not have let them switch to the modcon because we had enough water content with the ergomax to buffer the on/off heating cycles from the original cast iron unit and there is a lot less to go wrong with a cast iron boiler. Plus, you don't have to worry about condensate neutralization. Our current radiant floor fire tube boiler condenses all the time, but I really don't think it's worth the trouble for smaller apartment buildings and single family homes. A couple service calls (if you are not handy) blows your savings from the modcon. I'm not convinced the total life cycle monetary and carbon cost is worth it with the modcons.
If we ever replace anything, I would just get a modulating cast iron unit for the heating and on/off cast iron for DHW.
I hope this perspective helps.0 -
The financials depend so much on fuel costs that it's difficult to generalize, but my experience is that fire-tube mod/cons which are properly sized, installed, and commissioned require minimal maintenance (condensate trap cleaning once or twice a year.) The 30% minimum real world fuel savings they provide would make even a five-year replacement affordable in many cases. We'll know more in the next few years as the early installs get older, but so far they are doing just fine in the field.2
-
I should have added I'm in the Bay Area of California, so it doesn't get cold at all. We pay about $2/therm and $0.40/kWh after the initial tier allotments, which are pretty small.SWEI said:The financials depend so much on fuel costs that it's difficult to generalize, but my experience is that fire-tube mod/cons which are properly sized, installed, and commissioned require minimal maintenance (condensate trap cleaning once or twice a year.) The 30% minimum real world fuel savings they provide would make even a five-year replacement affordable in many cases. We'll know more in the next few years as the early installs get older, but so far they are doing just fine in the field.
0 -
-
Don't forget earthquakes.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements