Real Life Heat Loss Analysis by Observation??
WalnutFarmer
Member Posts: 48
A month or so ago, you all helped me educate myself on how to do a quasi Manual J heat loss in preparation for my conversion to gas. Now I've learned that the gas company is putting our project on hold until spring due to some environmental questions they need to address.
Since I now have a heating season between now and the conversion and since I know calculated heat loss is an educated guess, is there any way for me to evaluate actual heat loss by monitoring my oil burner activity over the winter months?
System is hydronic baseboard with Weil McClain oil burner and boiler with hot water coil.
Thanks for your continued help!
Since I now have a heating season between now and the conversion and since I know calculated heat loss is an educated guess, is there any way for me to evaluate actual heat loss by monitoring my oil burner activity over the winter months?
System is hydronic baseboard with Weil McClain oil burner and boiler with hot water coil.
Thanks for your continued help!
0
Comments
-
Yes.
You need an average temperature for a set amount of days And your actual fuel used to start. The rest is math which I've seen it done here and elsewhere. So I think you need to top off the oil tank run it for the month And re top off counting exactly how many gallons used0 -
Take a look here, here is a way to find the actual fuel usage and you don't even need to wait for this coming heating season.
mechanical-hub.com/sites/hydronics/heat-loss-calculation-on-every-residential-boiler-replacement/Dave Holdorf
Technical Training Manager - East
Taco Comfort Solutions
2 -
I can vouch for the above method coming close to a detailed manual j on our house. I did the math method using actual fuel consumption and it came within 2-3K of the Manual J report from the energy audit company we hired. Seems like a viable alternative as long as things like supplemental heating are factored in.0
-
I did a manual J and heat loss by useage its with in 5k btus of each other.0
-
Thanks all. Will give it a try.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements