Burnham ALP105 gas boiler repair
heatingFun
Member Posts: 84
My 7 years old Burnham ALP105 gas boiler stopped working for us few days ago. It worked 2 weeks ago. The fault information from the boiler screen are these:
Active faults,
Hard lockout 19
Purge rate providing failed
Possible cause: misswired fan power harness,
Misswired fan speed harness,
Defective fan
From its service manual and installation manual, I found the following for above information:
E 19 --- MCBA return sensor detected temperatures in
excess of 200°F for an extended period of time
--Lockout Number :: 19, Purge rate proving failed -- condition::
Blower is not running at Purge rate
when it should or fan speed signal not
being detected by Sage2.1.-- Possible Cause::
• Loose connection in 120 VAC fan wiring.
• Loose or miswired fan speed harness.
• Defective fan
A plumber from a company told us we need to replace the "fan motor assembly". The total cost will be about $1700.
Did some research and found this possible parts: http://www.supplyhouse.com/Burnham-101527-01-Blower-Alp-80-105
I am asking your help for the following questions:
1. Is that the right parts?
2. Do we need to replace the entire thing or just a fan replacement will be enough?
3. Is it a possible job for a handyman?
Thanks,
Active faults,
Hard lockout 19
Purge rate providing failed
Possible cause: misswired fan power harness,
Misswired fan speed harness,
Defective fan
From its service manual and installation manual, I found the following for above information:
E 19 --- MCBA return sensor detected temperatures in
excess of 200°F for an extended period of time
--Lockout Number :: 19, Purge rate proving failed -- condition::
Blower is not running at Purge rate
when it should or fan speed signal not
being detected by Sage2.1.-- Possible Cause::
• Loose connection in 120 VAC fan wiring.
• Loose or miswired fan speed harness.
• Defective fan
A plumber from a company told us we need to replace the "fan motor assembly". The total cost will be about $1700.
Did some research and found this possible parts: http://www.supplyhouse.com/Burnham-101527-01-Blower-Alp-80-105
I am asking your help for the following questions:
1. Is that the right parts?
2. Do we need to replace the entire thing or just a fan replacement will be enough?
3. Is it a possible job for a handyman?
Thanks,
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements