oil burner pressure gauge

panther
panther Member Posts: 6
edited October 2016 in THE MAIN WALL
Oil boiler with water radiators I may have some air in the system still and when I run the boiler pressure gauge doesn't move It's on 0 the circulator pumps working cuz I feel the pipes getting hot is there a way to check the pressure gauge or is the gauge be working and I have no pressure for some reason can I change the pressure gauge without draining the system thank you very much I assume if I run the system that it must have some pressure in it if the hot water is moving thank you very much

Comments

  • Eric_32
    Eric_32 Member Posts: 267
    It's called a tridicator. You will have to get the system to zero psi and be fast in the swap. close all vents and or auto vents so the system goes into vacuum then swap away. You can also get a psi gauge with hose adapter and screw on the boiler drain or any other drain in the system to show pressure. like this one (but try to get a gauge with a lower scale like max of 60-psi) : http://www.pft-alexander.com/uploads/6/0/4/1/60417059/s782439612586594443_p61_i1_w400.jpeg
    Bob Bona_4
  • panther
    panther Member Posts: 6
    Thanks Eric would it be dangerous to run it with the gauge not working properly would the pressure relief valve just go off don't you think I must have pressure if the systems running or could there be too much air in the system to create pressure thank you