Cracked Boiler - Warranty Claim?
I just bought my first home this past June. It has an oil fired Smith Series 8 steam boiler that is used for heat and DHW. Yesterday I noticed a sudden drop in the water level. I slowly added water and it all leaked out on the floor so I shut it down and pulled off the jacket and it looks like the flange between the boiler and tankless coil has cracked.
http://imgur.com/HEp6h98
http://imgur.com/CwRymJT
The boiler is still under warranty for the next 3 months. I contacted Smith and they told me this is not covered due to the corrosion.
Is this worth appealing?
Thanks!
Comments
-
IIRC that warranty is pro-rated, so you wouldn't get much anyway.
But that's the first time I've seen one of the older 8 series boilers fail. In general they're built like tanks.
Do you have natural gas available?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
No natural gas. Any chance of repair?0
-
Oh - and the warranty is 100% up to 10 years and then it is prorated, but if I understand correctly it is only for parts not labor.0
-
Not sure who you would appeal to?0
-
That was probably leaking for a good while before it failed, did you have it inspected before buying the house?
When replacing a boiler the labor is the lions share of the cost, you could just replace that section but it's still going to cost a lot of money.
Nobody likes to hear this but unless you can do the work yourself start looking for a new boiler.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
The inspector did point out the corrosion around the inlet to the coil. Prior owner showed that it had been serviced every year so at worst I expected that the coil may need to be replaced. I wasn't worried about the integrity of the boiler itself given that it was <10 years old.BobC said:That was probably leaking for a good while before it failed, did you have it inspected before buying the house?
When replacing a boiler the labor is the lions share of the cost, you could just replace that section but it's still going to cost a lot of money.
Nobody likes to hear this but unless you can do the work yourself start looking for a new boiler.
Bob
Edit: I'm not sure what is involved with replacing the coil, but I would entertain DIY if it is possible. I've done engine rebuilds, basic mig welding so I am mechanically inclined. A quick search shows that the coil is about half the cost of a new boiler....0 -
I sent Smith the pictures and they called saying that due to the corrosion they didn't consider it a warranty issue. I didn't make a counter argument, but I am surprised that a boiler that is maintained every year fails after <10 years. I'm sure I could press the issue if there is a legitimate argument that this is a manufacturing defect.MikeSpeed6030 said:Not sure who you would appeal to?
0 -
Very odd to see it crack there.... Just because it was "maintained" does not mean it was maintained right. Having the burner checked and vacuumed out is only part of the process. Was it flushed out? How about the water quality?0
-
True. All I've got to go on is the paperwork saying it was "serviced." I'm on town water in Massachusetts.kcopp said:Very odd to see it crack there.... Just because it was "maintained" does not mean it was maintained right. Having the burner checked and vacuumed out is only part of the process. Was it flushed out? How about the water quality?
0 -
That corrosion is long term not in the past year or 2. It was maintained to whose standards? My guess someone with low standards. That corrosion should have been addressed, but the previous homeowner or the service company decided to ignore it and leave you holding the bag. This is why Smith is telling you it's not warranty, lack of care isn't their fault.CrackedSmith said:
I sent Smith the pictures and they called saying that due to the corrosion they didn't consider it a warranty issue. I didn't make a counter argument, but I am surprised that a boiler that is maintained every year fails after <10 years. I'm sure I could press the issue if there is a legitimate argument that this is a manufacturing defect.</p>MikeSpeed6030 said:Not sure who you would appeal to?
Not sure of a DIY solution to this, the cast iron block looks to be cracked. By the time you buy a new coil and a new cast iron section and replace it you will be in for almost if not as much as a new replacement.
Where are you located? We may be able to recommend a good steam contractor in your area to come have a look and advise you.0 -
-
-
@Steamhead
When did the move the coil to the side of the boiler on the Series 8? That bolt, open to the side of the casting is a bad design. They'd have been better off to go to the back of the casting with a heavy duty washer.
Or, has that always been the configuration for steam?0 -
On steam it's always been there. The front plate location is above the waterline on a steamer, so it wouldn't work there.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
-
-
That crossed my mind as well. I wonder if the previous owner noticed the leak and got out their socket set and cranked on it. Strange thing is it was holding steam for a month or two after I bought the house and seemed to crack suddenly.Fred said:It really looks to me like someone kept cranking on the bolts, hoping to draw it up enough to stop the leaking. They cranked until they cracked.
Right now it is shutdown and we are without hot water. Is there any way to jury rig it until I can get it replaced? JB Weld?0 -
At this point, it sounds like Smith isn't going to do anything. With three months left on the warranty they'll probably just try to run out the clock. Given the experience one of our clients has had with a 28A leaking at the gaskets, this doesn't surprise me.
And there is a fair question whether a replacement section is even available, since they changed the 8 series over to a re-branded Peerless WBV several years ago.
You might be better off just replacing it with a Burnham MegaSteam, which is available with a tankless coil. The MegaSteam is the most efficient residential steamer out there, and the easiest to maintain.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting2 -
Sounds like I should give up on the repair / warranty. The soonest I can get a HVAC contractors in for an estimate is beginning of next week. I've got the wiring in place for an electric HW heater so I'm considering putting one in which takes some of the pressure off the boiler replacement time line. Electric HW should be more efficient than tankless coil right? I think I could also run the supply line through the new boiler so that there is less electric use in the winter?Steamhead said:At this point, it sounds like Smith isn't going to do anything. With three months left on the warranty they'll probably just try to run out the clock. Given the experience one of our clients has had with a 28A leaking at the gaskets, this doesn't surprise me.
And there is a fair question whether a replacement section is even available, since they changed the 8 series over to a re-branded Peerless WBV several years ago.
You might be better off just replacing it with a Burnham MegaSteam, which is available with a tankless coil. The MegaSteam is the most efficient residential steamer out there, and the easiest to maintain.0 -
It may well be that it was cranked down so much that after a couple months of expansion/contraction from heating cycles to heat water, the cast iron finally gave out. If I were any boiler manufacturer, I too would have a hard time feeling like that was a boiler flaw/defect. I might make some concession for the sake of "Good Will" but that would be just that, "Good will" for the sake of customer relations.CrackedSmith said:
That crossed my mind as well. I wonder if the previous owner noticed the leak and got out their socket set and cranked on it. Strange thing is it was holding steam for a month or two after I bought the house and seemed to crack suddenly.Fred said:It really looks to me like someone kept cranking on the bolts, hoping to draw it up enough to stop the leaking. They cranked until they cracked.
Right now it is shutdown and we are without hot water. Is there any way to jury rig it until I can get it replaced? JB Weld?
If it were me, I'd put that standalone water heater in. I think they are a much better solution than having the boiler run year round, 6 to 9 months of which is just for hot water. JMHO0 -
Are the new Smith boilers any good? Wondering if they would offer a discount on a replacement unit.Fred said:
It may well be that it was cranked down so much that after a couple months of expansion/contraction from heating cycles to heat water, the cast iron finally gave out. If I were any boiler manufacturer, I too would have a hard time feeling like that was a boiler flaw/defect. I might make some concession for the sake of "Good Will" but that would be just that, "Good will" for the sake of customer relations.CrackedSmith said:
That crossed my mind as well. I wonder if the previous owner noticed the leak and got out their socket set and cranked on it. Strange thing is it was holding steam for a month or two after I bought the house and seemed to crack suddenly.Fred said:It really looks to me like someone kept cranking on the bolts, hoping to draw it up enough to stop the leaking. They cranked until they cracked.
Right now it is shutdown and we are without hot water. Is there any way to jury rig it until I can get it replaced? JB Weld?
If it were me, I'd put that standalone water heater in. I think they are a much better solution than having the boiler run year round, 6 to 9 months of which is just for hot water. JMHO
Would be nice if they made the same model so that all of the connections could be reused :-(0 -
Make sure you are getting a competent steam contractor and not just any HVAC company. Steam has a lot of details that need to be correct in order to perform correctly. You are in Massachusetts @Charlie from wmass is in MA, but not sure if he serves your area? Where in MA? Charlie will travel.CrackedSmith said:
Sounds like I should give up on the repair / warranty. The soonest I can get a HVAC contractors in for an estimate is beginning of next week. I've got the wiring in place for an electric HW heater so I'm considering putting one in which takes some of the pressure off the boiler replacement time line. Electric HW should be more efficient than tankless coil right? I think I could also run the supply line through the new boiler so that there is less electric use in the winter?
Also if you post pictures of your current boiler and piping we may be able to give you an evaluation of if what you have is even close to correct.
0 -
Yes I go there. It is Massachusetts. Just not sure how far it is from home. It would be great if it were in the 413 area code. Been in 978 and 508 a lot this year.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
As @Steamhead said, the new Smith boilers are a re-branded Peerless. Peerless makes a good quality series of steam boilers, but the Burnham Megasteam is considered probably a top of the line oil boiler. Having said that, i understand your interest in maybe getting some kind of discount from Smith, on a replacement. Hopefully Steamhead or one of the other Pros will give you some feedback on the quality/longevity of the current Smith product(s).0
-
We haven't used one of the later Smiths. Since the OP doesn't have gas available, the MegaSteam is the way to go.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
I still like my Weil Mclain sgo boilers incase gas does become available.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
Thanks for all the help. I'll post pictures of the plumbing when I get home tonight.
Is there a "value" boiler recommendation versus "the best." Due to some changing personal situation I'm not sure that we will be in the house long term so I won't necessarily reap the long term benefits of the highest efficiency device / longest lasting.0 -
Sent you an email.Charlie from wmass said:Yes I go there. It is Massachusetts. Just not sure how far it is from home. It would be great if it were in the 413 area code. Been in 978 and 508 a lot this year.
0 -
My argument with this is how easy the Megasteam is to clean vs taking all of the sheet metal screws out and pulling the top off of the SGO. What a nightmare.Charlie from wmass said:I still like my Weil Mclain sgo boilers incase gas does become available.
Honestly, if I ever need a new steamer I might go with a Megasteam and gas gun just because, 3 pass.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
1 -
Screw gun and magnetic parts holder. Honestly I install both. If they are properly set up both are easy to clean.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
The Burnham you open the doors to clean.Charlie from wmass said:Screw gun and magnetic parts holder. Honestly I install both. If they are properly set up both are easy to clean.
No screw gun or parts holder. No?Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
4 bolts on the back, open door, remove baffles, and take off breeching. SGO has a swing out door too btwCost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
You don't pull the 4 screws off the top and pull the top off to brush down the sections?Charlie from wmass said:4 bolts on the back, open door, remove baffles, and take off breeching. SGO has a swing out door too btw
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Installing a new rear section today.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
On the OP's boiler?Charlie from wmass said:Installing a new rear section today.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
1 -
YesCost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating1 -
How'd you manage that? I thought replacement sections for older 8 series boilers weren't available....................All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
I guess I'll find out in a minute if it doesn't fit. Westfield is going to get one hell of an angry call from this ScotsmanCost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating2 -
Charle's attitude just went from "What an awesome Friday, let's get this done" to "oh, great, I hope this works......"
I hope it works out.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
No attitude still goodCost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating2
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements