Another header vs riser size thread
curiousburke_2
Member Posts: 70
I know similar questions have been addressed many times before, but maybe not exactly this one.
I'm likely getting a Peerless 63-04L installed; the specification is for 2 2" risers into a 2.5"header. I want to step the header up to 3" and make it a drop header. That could be fed by 2 2" risers, but I think the tappings for the risers are 3", so I'm wondering if there is a disadvantage of using 2 3" risers, the same as the header.
I can see that having the same riser size will cause the steam to speed up in the header. However, the steam velocity in the header still wouldn't be any faster than with the 2" risers, would it? Is it the absolute steam velocity or the reduction in velocity that causes water to drop out?
Thanks in advance!
I'm likely getting a Peerless 63-04L installed; the specification is for 2 2" risers into a 2.5"header. I want to step the header up to 3" and make it a drop header. That could be fed by 2 2" risers, but I think the tappings for the risers are 3", so I'm wondering if there is a disadvantage of using 2 3" risers, the same as the header.
I can see that having the same riser size will cause the steam to speed up in the header. However, the steam velocity in the header still wouldn't be any faster than with the 2" risers, would it? Is it the absolute steam velocity or the reduction in velocity that causes water to drop out?
Thanks in advance!
0
Comments
-
Thanks! I expected you to say I should put in a 4' header if I use 3" risers, and that using the same size was a no-no0
-
If I went with 2 2" risers, it seems like the steam velocity is actually higher than 1 3" riser. Which is preferred?
And yet another question: I could have a 4" black iron header for about the cost of a 3" cast iron header (actually, less if it's imported iron) ... opinion?0 -
With that size boiler I would do it all in 3", including risers.New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com0 -
Thanks! All the possible configurations is really interesting to me. I would love to assemble the fittings myself, but don't feel like I could tackle some aspects of the job.
A little piece of me is still saying "get the SlantFin and 25 year warranty", and this 2x2" vs 1x3" issue raises that specter. I leaned away from SlantFin because of the single 2.5" riser; was that a poor deciding factor?0 -
My EDR is 330 to 350, depending on this one radiator I've never been certain about, but then I have uninsulated mains in a basement that I like to stay warm. You estimated 390 including the main in my other thread.
With a 33% margin built in for average piping/pickup, I would think the 7% bigger GXHA-160 wouldn't make much of a deciding factor.
0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements