When The Header Is Smaller Than The Supply Mains...
New England SteamWorks
Member Posts: 1,525
Things don't work out too well...
New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com
0
Comments
-
The installer must have had small handsAll Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting3 -
Would you call that a "double header"?0
-
Someone went to a lot of extra effort to do it wrong didn't they? With all the new piping I see they could have brought those mains down to the new header individually and with roughly the same amount of pipe and fittings they used. At least the piping on the boiler looks like minimum spec...if you ignore pipe sizes. lol0
-
So, what if we were to Holohanitize it?
Something like this perhaps?
New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com4 -
Nice! And of course they could tell the difference right away when you started it up..................All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Add a header for the vaporstat and low pressure gauge...
New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com0 -
And maybe a little extra venting...
New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com0 -
All set for winter!New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com0 -
Too Nice!0
-
Hey RI, can you post back around January with a performance update? Maybe a little before/after gas usage, plus some happy comments from the homeowner.
ThanksThere was an error rendering this rich post.
0 -
I will! Promise. The owner is very detail orientated (as you would expect from someone who has their boiler re-piped) and keeps records of usage by degree day. He promised to share the data with me. I was thinking though to wait until heating season was over to post it. If it's like my others, should see pretty big savings.New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com0 -
Beautiful repipe you got there @RI_SteamWorks0
-
Yes, outstanding repipe!gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
Fantastic job , just wow ..
hvacfreak
Mechanical Enthusiast
Burnham MST 396 , 60 oz gauge , Tigerloop , Firomatic Check Valve , Mcdonnell Miller 67 lwco , Danfoss RA2k TRV'sEasyio FG20 Controller
1
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements