made a mess trying to change strainer on 2 pipe
yoadrian
Member Posts: 1
in Oil Heating
Good evening everyone. New guy here from NY. I would like your opinion on the proper method to change a pump or strainer/filter on a two pipe. How do you clear the entire system of oil before cracking in to it? Went to "tune up" my system at home and had a bit of a scare after removing a strainer cover and the return line starting spitting oil out.
Thank you
Thank you
0
Comments
-
That was always an advantage of a J pump over a mini pump. No leak back. Sometimes shutting off the oil supply line, and run the burner until the flame goes out will push the oil back to the tank. You can also work quickly and use a pump to push it back. Why a 2 pipe system? That is old school, and not necessary in most cases. FYI, never install a shut off valve inline for a return
0 -
If a standard single-line system won't work here, use a TigerLoop. There is no longer any need whatsoever for a two-line oil-feed system.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
drop the oil filter
run the burner til it locks out (checking safety at the same time)
reset a time or two
use a cookie sheet to catch the oil
change that strainerThere was an error rendering this rich post.
0 -
Tank location in reference to the oil burner is important in answering this question. Is the tank in the basement, outside above ground or buried in the ground? How long are the fuel lines from the tank to the burner? If fuel continues to pour from the tank return line that exits the top of the tank and the return line terminates below the fuel level in the tank, a siphon condition exists and if you take this one step further.... what if the fuel line were to break unnoticed?
Get rid of the return pipe ASAP and install a fuel de-aerator like the Tiger Loop mentioned above. This way you will have a shut off valve to use every time you need to change the filter
If you can see the top of the tank and there is a union on the return line, you can loosen the fitting to break the siphon and only the fuel in the return tubing will spill (into a container or) on the floor.
If the return line is short enough. Drop the filter and operate the pump for a 45 second safety time (time it takes for the reset button to trip) may also break the vacuum by pumping air thru the return line.Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements