@ChrisJ
Tinman
Member Posts: 2,808
Comments
-
Hi Steve,
Thank you, coming from you I take that as quite a compliment!
I was trying to reduce the time, and more so the sound of the air rushing out of the vents when the boiler fires up with all of the piping still very hot. For example, after only being off for 5 minutes when it's below 0°F out running 3 CPH.
I can get steam to the end of my 29' main in less than 90 seconds from the time when the thermostat calls for heat on a night like that. Considering the time to open the damper, light the burner and start steaming the time to actually get steam down the main it self is likely around a minute. Before downsizing from an EG-45 to an EG-40 I had seen total times of less than a minute from the time the thermostat calls for heat.
My pressure never goes above 1" WC anymore, usually between 0.5" and 0.75". I have a pressure switch set to force the Ecosteam into hold mode for 10 minutes if I hit 1 ounce. It's never happened, not even during large setbacks or when the boiler re-fires a few minutes after shutting down.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment3
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements