Replace compression tanks?
Chuck_17
Member Posts: 145
Commercial boiler replacement. Just replacing the boiler and the main pump. The question is whether or not to replace the two (50 year old) 120 gallon compression tanks with a diaphragm type expansion tank.
The original design temperature was 230 deg if that makes a difference.
Opinion?
The original design temperature was 230 deg if that makes a difference.
Opinion?
0
Comments
-
If the original tanks are in good shape I'd leave them there. They don't have any moving parts to fail, as diaphragm tanks do.
The line to the tanks should be connected to the top of a good air separator. The size of the air separator will depend on the main pipe size leaving the boiler. This setup will direct air from the system up into the tank, maintaining its air cushion. A B&G Airtrol Tank Fitting will help keep air from migrating from the tank to the system- again without any moving parts. I believe Dan covers this in one of his books- maybe "Pumping Away"?
And speaking of Pumping Away, of course you should.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting2 -
Steamhead is right on the money.
If the budget is good, replacement of the airtrol's might be a good place to spend, with the addition of the airseperator he mentioned.
Make sure the piping from the airtrol to the tanks gets a good pitch upward on horizontal runs so the air can head that direction. Don't put anysort of valve in the horizontal that would trap air, like a reduced port model.
If the budget is even greater, replace the guage glass valves and SG, or rebuild the packing on all.
Make sure no one has any auto air vents in the system, or if they are there, valve them off. Good for fast/initial fill, not good to stay open during normal circulation on compression tank systems.0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements