Pressure rating of old Corto style radiators?

tim smith
tim smith Member Posts: 2,807
Anyone have a spec on what these and maybe American radiators were rated mwp?

Comments

  • Steamhead
    Steamhead Member Posts: 17,387
    AFAIK they never published pressure ratings, but they were intended for use on systems with safety valves that would open at no more than 15 pounds on steam or 30 pounds on hot-water. FWIW, when we test these rads we pressurize them to 30 pounds.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • tim smith
    tim smith Member Posts: 2,807
    Thanks Frank, I figured so but was wondering due to some of the midrise building that use hot water and may be running higher than that?
  • Steamhead
    Steamhead Member Posts: 17,387
    Sure they don't use steam boilers feeding heat exchangers on the various floors?