Pressure rating of old Corto style radiators?
tim smith
Member Posts: 2,807
Anyone have a spec on what these and maybe American radiators were rated mwp?
0
Comments
-
AFAIK they never published pressure ratings, but they were intended for use on systems with safety valves that would open at no more than 15 pounds on steam or 30 pounds on hot-water. FWIW, when we test these rads we pressurize them to 30 pounds.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Thanks Frank, I figured so but was wondering due to some of the midrise building that use hot water and may be running higher than that?0
-
Sure they don't use steam boilers feeding heat exchangers on the various floors?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service