replacing old 2 line in ground tank with new 275 inside tank. Should I use 1 or 2 lines ?
pacer
Member Posts: 1
see above
0
Comments
-
One line is enough. If more suction is needed (unlikely) use a TigerLoop at the burner.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
What Steamhead saidTo learn more about this professional, click here to visit their ad in Find A Contractor.1
-
What Frank and Robert said0
-
What Bill said.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
What Robert, Frank, Bill, and Chris said.0
-
Always good to see the sense of humor alive and well0