Fan Motor

I have a lennox J3-29 , HS6-311-T13
Can anyone help me with a replacement fan motor for this unit.

Comments

  • SteamheadSteamhead Posts: 13,484Member
    What make and model is the old motor?
    All Steamed Up, Inc.
    "Reducing our country's energy consumption, one system at a time"
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Baltimore, MD (USA) and consulting anywhere.
    https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc
  • GrahamMalcolmGrahamMalcolm Posts: 3Member
    I will have to remove the old one to find out.
    I was hoping someone had the specs for the unit.
  • JUGHNEJUGHNE Posts: 6,423Member
    It will have to be removed for repair anyway.
    Will the blade move freely, if not the bearings are toasted.
    If it moves freely there is a slim chance the run capacitor might be the only problem.....slim.

    You could remove the grill or mounting panel and haul the entire thing to a motor shop......include the capacitor with it.
    Mark the location of any wires you unhook.
    Sometimes removing the blade from the motor shaft is very difficult. Some people change the blade, motor and always a new capacitor. A cracked blade or one with loose rivets can ruin a new motor's bearings in short time.
  • GrahamMalcolmGrahamMalcolm Posts: 3Member
    Thank you for the advice Jughne
    The unit runs fine for about 15 min then it trips the breaker, the AC guy said right away that it was the fan motor, and that the compressor was good solid 15amps reading.
    Also the blade does moves freely.
    Any chance it's just the capacitor.
  • JUGHNEJUGHNE Posts: 6,423Member
    If there was an AC guy there he should have checked the capacitor, fan motor might not even start with bad cap.
    Less chance of cap at fault.
    Did he measure amp draw on fan motor?
    A motor that small can trip a breaker only so many times before the smoke comes out of it.
  • John Mills_5John Mills_5 Posts: 935Member
    Call the Smithsonian! That sucker is OBSOLETE!
  • aircooled81aircooled81 Posts: 194Member
    Condenser fan motor is important to match the RPM.
    I think it is best advised you read the nameplate and match like for like. This is a good time to see if you can save the condenser fan blade, for reuse.
    You will need just, the RPM, Voltage, phase (likely single phase), frame, and horse power.
    Tell them you will want a new capacitor to match the new motor.