Sizing expansion tank for commercial systems
Wayco Wayne_2
Member Posts: 2,479
I'm looking to size an expansion tank for a new boiler change out we are doing. It will have 4 boilers @400K input each. I'm a little out of my comfort zone here. I had a good feel for residential, but this commercial sized stuff I feel limited. How should I proceed?
0
Comments
-
It is mainly about system volume, both Amtrol and Wessels have commercial tank sizers online.
http://westank.com/calculator/
The boiler output has some effect on the sizing of the pipe connection to the tanks. The Amtrol Engineering Handbook has a formula for that calculation.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Being a change out, there would have been a tank there for comparison purposes? New boilers might hold less water than old. That is if that is the only thing changed.0
-
Commercial boiler installations require an ASME certified expansion tank. Size according to load and system volume using the sizing charts on Amtrol's website. If the tank is undersized, there's risk of blowing off the relief valves.0
-
I just measured all the pipes in the system and converted into gallons. 278 gallons, not including boilers. The boilers are 4 Laars copper fin boilers @ 400K each. The height of the system is less than 10 feet. I looked at a vertical bladder tank on the Amtrol site but it said it was a non ASME tank. Not what I want. I feel like I'm getting close.0
-
The threshold where an ASME expansion tank requirement kicks in varies a bit by jurisdiction, so read the fine print.
The calculator link Bob posted above (or this one) will get you a solid answer on sizing if you input your minimum and maximum temps. Don't forget the water volume in the emitters and boilers.0 -
Look at multiple tanks also, sometimes the smaller tanks connected together end up being less $$, if it is a common off the shelf size.Wayco Wayne said:I just measured all the pipes in the system and converted into gallons. 278 gallons, not including boilers. The boilers are 4 Laars copper fin boilers @ 400K each. The height of the system is less than 10 feet. I looked at a vertical bladder tank on the Amtrol site but it said it was a non ASME tank. Not what I want. I feel like I'm getting close.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements