vacuum condensate lift fittings
garynavo
Member Posts: 1
Anybody know if these are still made? I'm looking at a project in California that needs them.
0
Comments
-
Can you describe the situation a bit more, as there may be an alternative solution.--NBC0
-
I've checked around, and have been told manufactured lift fittings have not been on the market for maybe 50 years or more. I only recall seeing one installation that had manufactured cast iron lift fittings, and that went in before WW 2.
These can be easily made up from common pipe fittings; either screwed or welded up.
The most important one is at the bottom of the lift. This is basically an inverted P trap. This allows the upstream horizontal run to totally drain. The upper loop over is only necessary if the downstream run is longer than 10 feet.
The actual lift pipe should be smaller in diameter. This increases the velocity in the lift and is more efficient.
Please keep in mind that lift fittings should only be used out in the system, and never just ahead of a vacuum condensate pump's receiver tank.
When a lift is required at the inlet of the vacuum condensate pump's receiver tank, an auxiliary accumulator tank with float switch should be used. This is really a large volume lift fitting with a float switch and air vent pipe with pressure vent check valve.
With this arrangement, the condensate flows by gravity to the auxiliary accumulator tank. If the vacuum pump is running, condensate immediately gets lifted up to the vacuum pump's receiver.
If the vacuum pump is not running, the aux tank will fill until the float switch trips, turning on the vacuum pump to make the lift.
If a lift fitting is used in lieu of an auxiliary accumulator tank, it will be necessary to run the vacuum pump continuous to keep the lower returns drained of condensate.
In this arrangement, when the vacuum pump shuts off, the pressure differential needed to make the lift is lost, and the lower returns will fill with condensate until the vacuum pump is started again. This will also cause a water seal on the system, preventing air from venting off to atmosphere.
Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
Website: www.nashjenningspumps.com
The first step in solving any problem is TO IDENTIFY THE PROBLEM.0 -
That should read.........P trap, not inverted P trap. Sorry.Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
Website: www.nashjenningspumps.com
The first step in solving any problem is TO IDENTIFY THE PROBLEM.0 -
thats a great little write up on how things work Pumpguy , much appreciated.gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
I can't tell you how many times I see this stuff piped wrong. As with what I read here about boiler installations, It seems like people don't read installation instructions, or do and just don't care.Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
Website: www.nashjenningspumps.com
The first step in solving any problem is TO IDENTIFY THE PROBLEM.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements