connecting copper tube with corrugated stainless
hot_rod
Member Posts: 23,399
Corrugated stainless is commonly used in solar thermal piping. Common connections flatten the end for a gasket joint, or flare it.
Both can be tough connections to seal glycols.
I've found with a 3/4" CTS expander tool you can slide the copper tube into the CSST.
I've tried a few brazing methods with a typical Mapp gas turbo torch tip. Plain brass rod, with flux added also works.
Now you can soft solder the copper tube, pressfittings, compression, etc. into the collector or other piping connections
Both can be tough connections to seal glycols.
I've found with a 3/4" CTS expander tool you can slide the copper tube into the CSST.
I've tried a few brazing methods with a typical Mapp gas turbo torch tip. Plain brass rod, with flux added also works.
Now you can soft solder the copper tube, pressfittings, compression, etc. into the collector or other piping connections
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream
trainer for Caleffi NA
Living the hydronic dream
3
Comments
-
Where I work we make copper to stainless or copper to black pipe connections pretty regularly. I personally don't work in that department by they use an acid based flux with 50% silver solder. After clean up, the joints look beautiful and we test at pressures up to 350 PSI.
Nice work.0 -
I love using 45%. I use it all the time in refrigeration or comfort cooling.0
-
Is that a workbench made of old hardwood flooring?Steve Minnich0
-
Grizzly Tool is near me, I drop by their seconds outlet and pick up the damaged tops. 100- 150 bucks depending on size and damage.Stephen Minnich said:Is that a workbench made of old hardwood flooring?
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Nice work.
I'm curious how you deal with expander grease on the inside of the CSST?0 -
Nice! I like it, I've melted a fair share of Harris rods as well. I do love all things brazed or soft soldered, especially if glycol is in the mix. Great tip hr.
SFMServing Northern Maine HVAC & Controls. I burn wood, it smells good!0 -
I use some grease on the backside of those segments, nothing on the outside. You want to clean both surfaces, belt sander and fitting brush, is what I usedSWEI said:Nice work.
I'm curious how you deal with expander grease on the inside of the CSST?
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements