I have 2 furnaces in my house, both Trane XE78. One of them needed a new control board, a White-Rogers replacement. Now when I go to turn on the fan to circulate air through the house, the compressor fan outside turns on instead. I've compared the control boards in both furnaces and the wires are not all connected to the same ports.
The old furnace board wires are as follows:
Cool - black wire
Heat - blue
Park - red
Park - yellow
Line - black
XFMR - black
The new furnace board wires are:
Cool - black wire
Heat - blue
Park - yellow
Fac - red
Line - white
XFMR - black
My question has to do with the red wire. There is another Park port on the new board and I'm wondering if the red wire is simply on the wrong port, the Fac port. I'm afraid to switch it, though, because I don't want to short out the board and have to buy a new one. Can anybody help?
The old furnace board wires are as follows:
Cool - black wire
Heat - blue
Park - red
Park - yellow
Line - black
XFMR - black
The new furnace board wires are:
Cool - black wire
Heat - blue
Park - yellow
Fac - red
Line - white
XFMR - black
My question has to do with the red wire. There is another Park port on the new board and I'm wondering if the red wire is simply on the wrong port, the Fac port. I'm afraid to switch it, though, because I don't want to short out the board and have to buy a new one. Can anybody help?
0
Comments
-
G is back feeding through the thermostat to Y. Check low voltage wiring at control board and thermostat.
Isolate Y on the control board or install isolation relay.0 -
I believe the terminal designations that the o.p. listed are line voltage connections to the board for power and fan speeds. It looks like the low speed red wire just needs a park ( unused ) terminal. If nothing is available just tape it off as to isolate it. Do not use the EAC terminal for a fan speed connection , that red wire does not belong there.
The terminal labled " line " needs to be 120 vac HOT , whatever color that is so be it.( Edit : it looks like both the line AND xfmr may require 120 vac HOT ). Be careful and good luck !!!hvacfreak
Mechanical Enthusiast
Burnham MST 396 , 60 oz gauge , Tigerloop , Firomatic Check Valve , Mcdonnell Miller 67 lwco , Danfoss RA2k TRV'sEasyio FG20 Controller
0 -
Your problem is with the low voltage wiring.0
-
Thanks guys! Got it all working with your help!0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements