teledyne jvt100c boiler

1955
Member Posts: 1
in Gas Heating
my gas valve and pump turn on but after 4-10 seconds turn off. I changed the pump relay, did not make a difference.
Zone valves are open, pump runs fine when wired direct. any thoughts welcome
Zone valves are open, pump runs fine when wired direct. any thoughts welcome
0
Comments
-
heat exchanger sooted up? roll-out switch tripping?0
-
What is the gas pressure? before and after start up?0
-
Make certain there is a good ground between the pilot assembly and the gas valve. That's a Honeywell Smart Valve if I am not mistaken and it is very susceptible to poor ground problems and loss of flame signal. You really need a digital multi meter to see what it is that is causing flame loss. If you don't have that ability, should hire someone who does..
After re-reading your post, it appears the short cycling may be coming from the thermostat. Check the anticipator setting on the thermostat.
ME0 -
FYI, the JVT100C is a standing pilot boiler, most likely from the 1980s. There may not be a rollout switch on a unit this old. If the pump shuts down and the gas valve closes at the same time, try jumping terminal R to terminal W on the outside of the boiler. If the boiler runs normally, the problem is most likely the thermostat, per ME.0
Categories
- All Categories
- 87K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 58 Biomass
- 426 Carbon Monoxide Awareness
- 113 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 109 Geothermal
- 161 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 994 Plumbing
- 6.3K Radiant Heating
- 391 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 55 Water Quality
- 44 Industry Classes
- 48 Job Opportunities
- 18 Recall Announcements