teledyne jvt100c boiler
1955
Member Posts: 1
in Gas Heating
my gas valve and pump turn on but after 4-10 seconds turn off. I changed the pump relay, did not make a difference.
Zone valves are open, pump runs fine when wired direct. any thoughts welcome
Zone valves are open, pump runs fine when wired direct. any thoughts welcome
0
Comments
-
heat exchanger sooted up? roll-out switch tripping?0
-
What is the gas pressure? before and after start up?0
-
Make certain there is a good ground between the pilot assembly and the gas valve. That's a Honeywell Smart Valve if I am not mistaken and it is very susceptible to poor ground problems and loss of flame signal. You really need a digital multi meter to see what it is that is causing flame loss. If you don't have that ability, should hire someone who does..
After re-reading your post, it appears the short cycling may be coming from the thermostat. Check the anticipator setting on the thermostat.
METhere was an error rendering this rich post.
0 -
FYI, the JVT100C is a standing pilot boiler, most likely from the 1980s. There may not be a rollout switch on a unit this old. If the pump shuts down and the gas valve closes at the same time, try jumping terminal R to terminal W on the outside of the boiler. If the boiler runs normally, the problem is most likely the thermostat, per ME.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements