Blast tube deterioration and CO
Andrew Rudin
Member Posts: 29
I thought that, normally, carbon monoxide is generated by lack of combustion air or flaky fire-side heat exchange surfaces. After correcting both in a Weil McLain model 578 low pressure steam boiler, CO remained over 2,000 PPM. So I pulled the burner to find that part of the end of the blast tube had been burned away. What would have caused this? Could the condition of the end of the blast tube cause high CO?
Was the boiler over-firing? Gas pressure?Steve Minnich0
Yes, the end of the blast tube being burned off could cause flame impingement and CO. The blast tube may have been too far in the combustion chamber. Usually should be flush to a little recessed from the combustion chamber. Combustion being off originally could cause the blast to overheat and corrode away. Just few notes, good luck.