Commercial DHW
Dan Foley
Member Posts: 1,264
This is one that Brian G., Poppy and crew have been working on for the last three weeks. We are replacing the DHW system in a 47 unit apartment building in DC. The current system uses a direct-fired tank connected to a 500 gal storage tank. The storage tank is leaking and they have been replacing the direct-fired tank at a rate of every two years.
The engineer designed a system around seven tankless heaters on a manifold. Due the hardness of our water, I did not like this design and proposed an alternate. My design of two Viessmann Vitodens connected to four 120 gal. stainless steel storage tanks was accepted by the board.
- DF
The engineer designed a system around seven tankless heaters on a manifold. Due the hardness of our water, I did not like this design and proposed an alternate. My design of two Viessmann Vitodens connected to four 120 gal. stainless steel storage tanks was accepted by the board.
- DF
0
Comments
-
Beautiful work, Dan (as usual.) I'm curious about the green-bodied valves above the Stratos pumps (below the butterfly valves) -- are those flowsetters of some sort?
Have you guys used the ETV on previous jobs? I like the concept, especially for hard water areas.0 -
Thanks, Kurt.
The green valves above the pumps are Taco triple-duty valves (flow check, balance, isolation).
https://www.taco-hvac.com/products/water_circulation_pumps__circulators/pump_accessories/plus_two_multi-purpose_valve_straight_patternangle_pattern/index.html
This is the first time we have used the ETV. The existing Leonard mixing valve station scales up and is re-built just about every six months due to hard water and scale.
Brian piped the new stainless steel mixing valve body with union connections and a spare valve body is included in the contract. If/when it scales up, it can be replaced in less than an hour.
- DF1 -
Similar experience here with a couple of large Symmons mixing valves. We recently replaced one of those with a homegrown ETV setup. Film at eleven.Dan Foley said:This is the first time we have used the ETV. The existing Leonard mixing valve station scales up and is re-built just about every six months due to hard water and scale.
0 -
Very nice work very professional.
I see you used Viega Propress copper fittings.
Have you ever used the Viega Megapress fittings for steel pipe for the gas lines?
Anyone else using the Viega Megapress fitting for gas lines and water lines? How do you like using the Megapress fittings.0 -
Thanks, Bob.
We have used mega press to re-pipe wet returns on steam systems. I have not used it for gas pipe as we rarely run gas.
- DF0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements