sight glass full
jim929
Member Posts: 1
hi my sight glass usually shows half full but now it completely full how do i fix this?
0
Comments
-
Could be clogged.......boiler could be overfilling....a little more details...pics of boiler and piping helpASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
Open up the boiler drain and see if you can remove water till it's at the right level. If water is coming out and the sight glass does not start to drop it could well be a clog in a sight glass cock.
If you have an auto water fill on the boiler it may be leaking by or maybe the LWCO has failed and it's telling it to fill when it shouldn't.
Pictures will help.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0