You wouldn't think it should spill without the baffle, I always assumed that was just to increase efficiency. Why was it removed?
IMO Something's wrong with the B vent assuming there's plenty of fresh air.
Paul, do you have a Dwyer 460?Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
No i have the bacharach insight plus which tests draft....it looks as if the water heater has always been spilling....there is a 6 in duct in the mechanical room for combustion air....there's 5 in b vent with 20 ft height ....the b vent is reduced to 4 inch then a 4 in t wye picks up the water heater first then the fan assisted furnaceASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
The 460 is nice because it's just a cheap small light gauge you can carry around without worrying about it getting lost, stolen, damaged etc.Paul S said:No i have the bacharach insight plus which tests draft....
I think the kit can be had on Ebay for $30 or so.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
This is what i found in the selkirk manual....its similar what i have there besides the fact that there is a 4 inch t wye ....instead of the full sized 5 in interconnection tee shown in the pic belowASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
The 4 inch TWY is insufficient. According to Table C4, Fan/Nat is minimum 5 inch up to 177K if there is no depressurisation.0
-
My problem with this is I highly doubt if code calls for 5" that a 4" would cause spilling.Henry said:The 4 inch TWY is insufficient. According to Table C4, Fan/Nat is minimum 5 inch up to 177K if there is no depressurisation.
Something still sounds wrong.
Obviously, as you're suggesting the whole thing needs to be brought up to code, but I doubt it's the only issue.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
I know that it calls for a common 5 in with 2 4in vent connectors. ...but when i have the furnace off....the water heater still spills....the water heater has 3 ft of conn rise....and to mention the draft hood on wh is not for this appliance it looks like they took it off the water heater it replaced...ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company1 -
What do you think you'll end up doing?Paul S said:I know that it calls for a common 5 in with 2 4in vent connectors. ...but when i have the furnace off....the water heater still spills....the water heater has 3 ft of conn rise....and to mention the draft hood on wh is not for this appliance it looks like they took it off the water heater it replaced...
New heater?
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
New heater and change all venting in mechanical roomASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
Not having the baffles in the flue ways is wasting a HUGE amount of energy. The thermal efficiency is probably hovering around 30%. Not sure if that would be contributing to the spillage, but I do suspect so because by not having the baffle in place, it is pulling HUGE amounts of air into the combustion process, and over powering the ability of the vent to handle the load.
Best to refer to the National Fuel Gas code as it pertains to vent size, vent connectors, fittings etc to make sure it is in compliance with the intent of the code, but you absolutely have to replace the baffle, if you can find one. If not, replace the whole heater.
No spillage is good spillage...
METhere was an error rendering this rich post.
0 -
What the roof termination look like? Good clearances?0
-
Thanks for all the comments guys....i wish took a before pic of the venting...below i posted the pic of the old heater you can see how discolored it is from the years of spillage....co readings were climbing well past 1500ppm before i took my analyzer out...new heater co air free ppm is 42ppm.. i resolved issue with venting and installed a new water heaterASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company1 -
Is there a light bulb in the cleanout for the evaporator drain!?
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Lmao...yes i removed itASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
You gotta go all in @Paul S, get yourself some press ball valves!0
-
I only had non potable water ones on my truck....plus i have so many sweat ones that i never use ....i use viega and legend valves for pressASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
You may have saved a life(s) and a lot of fuel. Congratulate yourself.
And they will have a bonus of more hot water as well.
WIN WIN WIN.
Good job.
METhere was an error rendering this rich post.
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements