CO alarm went off at low level
sunlight33
Member Posts: 378
Earlier this evening the CO alarm in my garage went off. I ran down from upstairs, thinking it was probably the smoke alarm, but it's the CO alarm showing 40 ppm on its display. Okay, I thought to myself: I don't have to hold my breath. I opened the garage door, checked the boiler and found the burner was rather off at that time (exhaust pipe runs through the garage), the alarm went away after five minutes but I don't know what might have triggered it.
0
Comments
-
What do you mean by "the burner was rather off" ?0
-
If a car wasnt running in the garage....i would shut the boiler down and have a professional come out to perform a combustion analysis with an electronic combustion analyzer. .
.where are you located?ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
I mean the boiler was not on at that time, so the pipe was not carrying flue gas. I drove my car back about half an hour prior to the alarm went off but I don't think I left the car running in the garage.
I am in New York.0 -
Is there a standing pilot? I would do as Paul S suggests and have someone come out and check it out.0
-
By nyc?....i service all 5 boroughsASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company1 -
No, upstate. I have someone to contact.
Thanks for the help.0 -
Is there a water heater in the garage?0
-
Nope, and everything's looking normal.0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements