Expansion Tank

LionA29
Member Posts: 255
I have a basement hydronic heating zone and wanted to know what PSI the expansion tank should be set at?
Amtrol model 30
Thank you for your help.
Amtrol model 30
Thank you for your help.
0
Comments
-
The pressure in the tank needs to be checked and adjusted before you connect it to the system. The pre-charge pressure will be the same as the pressure that you operate you system at. typically 12 psi is fine for residential homes 3 stories or less.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Then you need to bleed the system pressure to 0 PSI, then check and adjust pressure, then recharge system. If water comes out of the schrader valve, you tank has failed and needs to be replaced.
Fill pressure is based on system height above the boiler, (1/2 PSI per vertical foot of elevation) and then add 5 PSI to that figure,and adjust the expansion tank t match that figure. Typical 2 story house = 12 PSI.
ME1
Categories
- All Categories
- 86.9K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 425 Carbon Monoxide Awareness
- 109 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 105 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 975 Plumbing
- 6.3K Radiant Heating
- 386 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements