what happens if you sidewall vent a natural draft chimney

Joseph_4
Joseph_4 Member Posts: 293
i have a customer that i came to whose boiler was carbonized. very high co. I powerwashed boiler and took apart boiler.used my analyzer and co was down to 16 ppm. He has a dryer in the room and i figured that was the cause. When I got home it hit me that this was a natural draft boiler that was sidewall vented without a powerventer kit.
Will be calling manufacturer today. name was valiant. never heard of them before... To advise customer on either getting a power vent kit or b vent double wall chimney.

I never saw this done before and am wondering if that caused it to carbonize
Thanks
Joe Hardoon
HHI SERVICES LLC

Comments

  • John Mills_5
    John Mills_5 Member Posts: 952
    It must have a Field Controls or Tjernlund sidewall vent kit installed. May well be spilling flue gases into the basement this way.
  • captainco
    captainco Member Posts: 796
    However if you put a power venter on a boiler with a drafthood you may just kill your customer.
  • Steamhead
    Steamhead Member Posts: 17,384
    I think you mean the brand name was "Vaillant". Is this oil or gas?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Eric_32
    Eric_32 Member Posts: 267
    There were also power vented boilers that had built in draft inducer motors in them made to side wall vent.

    The ones we use to install were the Utica USC boilers. They used stainless pipe for the flue with a gasket and hose clamp at the joint. Nice boiler but as higher efficient models came around they disappeared.

    If it has a draft hood either external or built into the jacket it is a atmospheric boiler designed to vent into a chimney. Without a vertical chimney to create draft it would spill exhaust in the room.
  • Joseph_4
    Joseph_4 Member Posts: 293
    the boiler is a gas boiler vaillant. model number
    ga100-14 spvd
  • Paul S_3
    Paul S_3 Member Posts: 1,280
    Are you checking CO air free?
    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • Bob Harper
    Bob Harper Member Posts: 1,091
    For boilers for connection to gas
    vents or chimneys, vent installations
    shall be in accordance with Part 7,
    Venting of Equipment, of the
    National Fuel Gas Cede, ANSI
    Z223.1--Latest Edition, or applicable
    provisions of the local building
    codes.
    Must vent into an approved chimney or vent designed for CAT I appliances meaning it must terminate above the roofline and is NOT intended for sidewall termination. This is a death trap as is and illegal. Sure, it can cause sooting, CO, equipment damage, etc.
  • JUGHNE
    JUGHNE Member Posts: 11,276
    Am I following this correctly......this is just vented out the side wall without power venting.....maybe "B" vent pipe stuck out the side wall.....and it is an atmospheric burner??

  • Joseph_4
    Joseph_4 Member Posts: 293
    I checked with Valliant they have one employee left stopped manufacturing in us in 1996. Their only tech support passed away. The friendly employee sent me a manual and it seems clear this needs a regular chimney. The manual clearly states the ga-100 is a natural draft boiler and must not be connected to any mechanical draft system operating under positive pressure I guess that settles it leaving and need to build a chimney B vent
    thanks for all input
    Joe
    HHI Services LLC