what happens if you sidewall vent a natural draft chimney
Joseph_4
Member Posts: 293
i have a customer that i came to whose boiler was carbonized. very high co. I powerwashed boiler and took apart boiler.used my analyzer and co was down to 16 ppm. He has a dryer in the room and i figured that was the cause. When I got home it hit me that this was a natural draft boiler that was sidewall vented without a powerventer kit.
Will be calling manufacturer today. name was valiant. never heard of them before... To advise customer on either getting a power vent kit or b vent double wall chimney.
I never saw this done before and am wondering if that caused it to carbonize
Thanks
Joe Hardoon
HHI SERVICES LLC
Will be calling manufacturer today. name was valiant. never heard of them before... To advise customer on either getting a power vent kit or b vent double wall chimney.
I never saw this done before and am wondering if that caused it to carbonize
Thanks
Joe Hardoon
HHI SERVICES LLC
0
Comments
-
It must have a Field Controls or Tjernlund sidewall vent kit installed. May well be spilling flue gases into the basement this way.0
-
However if you put a power venter on a boiler with a drafthood you may just kill your customer.0
-
I think you mean the brand name was "Vaillant". Is this oil or gas?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
There were also power vented boilers that had built in draft inducer motors in them made to side wall vent.
The ones we use to install were the Utica USC boilers. They used stainless pipe for the flue with a gasket and hose clamp at the joint. Nice boiler but as higher efficient models came around they disappeared.
If it has a draft hood either external or built into the jacket it is a atmospheric boiler designed to vent into a chimney. Without a vertical chimney to create draft it would spill exhaust in the room.0 -
the boiler is a gas boiler vaillant. model number
ga100-14 spvd
0 -
Are you checking CO air free?ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
For boilers for connection to gas
vents or chimneys, vent installations
shall be in accordance with Part 7,
Venting of Equipment, of the
National Fuel Gas Cede, ANSI
Z223.1--Latest Edition, or applicable
provisions of the local building
codes.
Must vent into an approved chimney or vent designed for CAT I appliances meaning it must terminate above the roofline and is NOT intended for sidewall termination. This is a death trap as is and illegal. Sure, it can cause sooting, CO, equipment damage, etc.0 -
Am I following this correctly......this is just vented out the side wall without power venting.....maybe "B" vent pipe stuck out the side wall.....and it is an atmospheric burner??
0 -
I checked with Valliant they have one employee left stopped manufacturing in us in 1996. Their only tech support passed away. The friendly employee sent me a manual and it seems clear this needs a regular chimney. The manual clearly states the ga-100 is a natural draft boiler and must not be connected to any mechanical draft system operating under positive pressure I guess that settles it leaving and need to build a chimney B vent
thanks for all input
Joe
HHI Services LLC0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements