Do I have the boiler replacement size correct?
pachysandra
Member Posts: 3
Hello everyone,
I want to be sure I am selecting the proper size steam boiler for my house, and so I came here to ask for you're help.
I have attached the replacement boiler sizing chart for my duplex, and a screen shot of the Burnham Independence Boiler specifications page.
I believe the PIN4PV is the closest size to what I need. Maybe a bit small, but the closest.
For what its worth, I installed 2ea. Gorton #2 vents at the end of the main, and insulated the main with 1" material.
Thanks for your comments.
I want to be sure I am selecting the proper size steam boiler for my house, and so I came here to ask for you're help.
I have attached the replacement boiler sizing chart for my duplex, and a screen shot of the Burnham Independence Boiler specifications page.
I believe the PIN4PV is the closest size to what I need. Maybe a bit small, but the closest.
For what its worth, I installed 2ea. Gorton #2 vents at the end of the main, and insulated the main with 1" material.
Thanks for your comments.
0
Comments
-
You need to calculate the EDR of your existing radiation to size the boiler properly. Do not, just match the size of what is there.0
-
I think he did that judging by his attachments. However, his choice, if he wants that particular boiler is a bit "undersized" by current standards. I think they're asking if it's still in the ballpark. OP, are you deadset on this brand boiler, is this what was there or what your installer prefers to put in?Two-pipe Trane vaporvacuum system; 1466 edr
Twinned, staged Slantfin TR50s piped into 4" header with Riello G400 burners; 240K lead, 200K lag Btus. Controlled by Taco Relay and Honeywell RTH6580WF0 -
-
Gerry Gill who Dan has mentioned in his books considers Burnham to the cadillac of steam boilers. So that's why I was looking at them.
My friend is a commercial plumber and we will install it together based on what I want to buy.
I should also mention that all the radiators are on the first floor. In other words, there is a lot less pipe in the system than if the pipe had to travel up to a second floor. So the "pick up factor" is less because the connected load is less. I believe this size boiler will be just right. But I just like asking for input. You never know what you can learn, unless you ask questions.0 -
Sure.......MegaSteam MST 2880
-
That's a oil boiler. I need a gas boiler. but thanks.0
-
That would still give you a 23% pickup factor. @ChrisJ is much lower than that and no problems. If it's only a single level house I would go for it. I am sure others will chime in.0
-
I'd use it.
Robert O'Connor/NJ0 -
I'd go with that too. 23% Pick-up is plenty and the next step up to the IN-5 is way to big. It should work well. Best of luck!0
-
If only they were all this simpleTwo-pipe Trane vaporvacuum system; 1466 edr
Twinned, staged Slantfin TR50s piped into 4" header with Riello G400 burners; 240K lead, 200K lag Btus. Controlled by Taco Relay and Honeywell RTH6580WF0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements