Weil Mclain Ultra
Lakewood
Member Posts: 7
I'm having a problem that my Weil Mclain ultra is not resetting. Error code U 1.25. Any suggestions?
0
Comments
-
Display shows U124 or
U125
Display stays on U124 or U125 1 Check transformer. If good:
s
Turn off power to the boiler.
s
Disconnect thermostat wires at boiler.
s
Replace F3 fuse.
s
Determine cause of fuse failure on 24-volt system.
s
Replace defective part and retry.
2 If problems persists, check low voltage terminal strip and wire harness.
Replace if necessary. Retry.
3 If problem persists, replace control module.
But it's usually the control module.
you should have received the updated control supplement which the above is directly from.0 -
Weil McLain Ultra Parameter Setting.
I have an oversized boiler, and reduced the perimeter 13 setting to 40, however, left the perimeter 15 setting to 52. Meaning, that my boiler did a DHW call should provide 190° heat, but it does not. It seems to be reduced to the fan speed I use for home heating. I checked the setting and it seems fine to me. Any suggestions?0 -
Why not start a new thread on this, for more clarity.--NBC0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements