How to calculate recovery rate for indirect DHW

Boon
Member Posts: 260
Hi. I'm trying to calculate the actual recovery rate for an indirect DHW given my boiler size. I think I'm missing something.
Cold water 40°F
Target 130°
∆T = 90°
90° * 8.34 = 750 BTU/gal
If the boiler is 55000 operating at 87% then I'm taking 47,850 BTU/hr ÷ 750BTU/gal = 63.8 gal/hour
But 63.8 gal/hour assumes that 100% of the 47850 is being transferred to the DHW and that can't be true. And I think the flow rate [between the indirect and the boiler] matters, too, but I don't know how to account for that.
Am I on the right track here?
Cold water 40°F
Target 130°
∆T = 90°
90° * 8.34 = 750 BTU/gal
If the boiler is 55000 operating at 87% then I'm taking 47,850 BTU/hr ÷ 750BTU/gal = 63.8 gal/hour
But 63.8 gal/hour assumes that 100% of the 47850 is being transferred to the DHW and that can't be true. And I think the flow rate [between the indirect and the boiler] matters, too, but I don't know how to account for that.
Am I on the right track here?
DIY'er ... ripped out a perfectly good forced-air furnace and replaced it with hot water & radiators.
0
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements