spirovent is leaking from the vent foaming glycol system
Options
stmary
Member Posts: 1
Can this be repaired or needs to be replaced?
0
Comments
-
Foam is hard for a vent tO deal with. Foaming glycol is often caused by dirty fluid conditions. You can buy anti foaming additives for glycol solutions. Or flush clean and start with fresh glycol, premixed with DI waterBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0