Trane 55AL Trap
SDSteam
Member Posts: 13
Ran across a Trane 55AL F&T Trap on campus the other day and have a couple of questions...
1:) Is this trap OK to be mounted on it's back? I couldn't find any definitive paperwork on this model and it didn't have the always helpful, glaring "up" or "down" markings on the trap.
2:) What is the consequence of it being installed incorrectly for at least 40 years?...
We still have a few rebuild kits left over for this model # of trap, so want to make sure this one is installed correctly...
1:) Is this trap OK to be mounted on it's back? I couldn't find any definitive paperwork on this model and it didn't have the always helpful, glaring "up" or "down" markings on the trap.
2:) What is the consequence of it being installed incorrectly for at least 40 years?...
We still have a few rebuild kits left over for this model # of trap, so want to make sure this one is installed correctly...
0
Comments
-
If the removable cover is not on top, it's installed wrong. In any other position it may constantly pass steam.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting2 -
-
Thanks!
That's how it's installed. I questioned it because I recently found a different brand/model trap in a crawlspace that was incorrectly installed with the cover up like that and passing steam.
Cleaned out and replaced the internals on this 55 and that took care of some of the issues in this building.0 -
Unless the cover on the Trane 55 series is up, the float won't work. Here's an internal photo of a spare I have:
The Tunstall cartridges work on this unit, to replace the brass bellows.0
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 97 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 930 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements