Honeywell T87F accuracy of thermometer

xpsd300
xpsd300 Member Posts: 3
Hi,

I'm replacing a Honeywell T87F thermostat that got damaged during our remodel with a direct replacement.

I have two NOS units and noticed that, laying flat in their boxes, the thermometer on one matches the room temperature, but the other is off by +6 degrees.

Does it sound like the second unit is defective, or does it just need to be recalibrated? The thermometer needle does move when brought from a hot to a cold space.

Does the T87F need to be installed on a wall to get an accurate room temperature reading?

Thanks.

Comments

  • bmwpowere36m3
    bmwpowere36m3 Member Posts: 512
    Is that the basic round model from honeywell (what used to be mercury-switch)? Mine holds the temp in the house correctly (setting), but it reads 4* low on actual temp (lower needle).

    Meaning when set to 68*, the house stays at 68* according to two digital thermometers. However it indicates the to is 64*...

    I've read a few reviews, with similar responses... the displayed/actual temp is way off. For me it's just a temp thermostat, till I find a nice hardwired, programmable one.
  • JUGHNE
    JUGHNE Member Posts: 11,279
    I think there was a procedure for recalibrating the thermometer, it may have involved a special wrench. Most people never worried about it and just set temp to be comfortable. (Before digital thermometers it was close enough)
  • xpsd300
    xpsd300 Member Posts: 3
    edited February 2016
    The spare T87 thermostats I have are mercury switches. They were manufactured in 2002.

    Last night, I found 4 old thermostats (circa 1980) tucked behind my oil burner and I did a test overnight.

    This morning, the old ones and one of the spares reported a room temperature of 68 degrees, which I confirmed to be accurate with a hand-held digital thermometer. But the other spare was still off by 6 degrees.

    Regarding recalibration, the instruction sheet with the 2002 units only mention using a 104994 Calibration Wrench in passing. I did find more detailed instructions online, but recalibration only appears to fix problems related to the mercury switch, not the room temperature thermometer.
  • JUGHNE
    JUGHNE Member Posts: 11,279
    edited February 2016
    Yes, I remembered that wrongly. Most never worried about the thermometer accuracy. Just get it level as in the instructions.
    If you wanted to use that T-stat, I would just buy some type of wall mount digital T-stat, maybe with the outdoor remote sensor and then you have it all in one place. Just ignore the HW T-meter, it has no function in operation. FIWM

    More important is the setting of the heat anticipator....shorter or longer cycles....do you have steam?
  • xpsd300
    xpsd300 Member Posts: 3
    So I figured out how to recalibrate the room temp thermometer after completely disassembling one of the old ones I had on hand.

    There is a screw located on the top of the dial beneath the "Honeywell" decorative button (see attached).

    To get access to it, carefully remove the plastic dome by inserting a small screwdriver into the notch on the face of the dial. Then, pry off the decorative button. Use a flathead screwdriver to rotate the room temp needle as needed. Finally, reinstall the decorative button and the plastic dome (the dome will crack if too much pressure is applied).

    Regarding the heat anticipator, I have a hot water oil burner with Taco 571-2 zone valves (0.9A rating). Setting the heat anticipator to 0.9 causes the heat to kick in when the room temp dips 1/2-1 degree below the set temp, which I find to be comfortable.

    I've tried a few mercury free thermostats in the past, but I've found it difficult to replicate the 0.9 setting.
    ChrisJTim Potter
  • JUGHNE
    JUGHNE Member Posts: 11,279
    Good work, the key word is "comfortable". I would recommend putting the digital thermometer in a drawer out of sight.
  • ChrisJ
    ChrisJ Member Posts: 16,316
    1/2 to 1 degree?
    I find it hard to believe this cannot be achieved with a Visionpro 800 series set to 2 or 3 CPH?

    The original T87 is a fine unit and I'm glad you shared how to calibrate the thermometer but I just find it hard to believe a quality digital thermostat can't replicate this performance if not better.


    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    Grallert
  • Canucker
    Canucker Member Posts: 722
    I haven't been able to equal the control my old t87 had for the basement zone. 2 cycles overshoots/undershoots by at least 1 degree celsius. I tried 3 and 4 cph but it ended up short cycling my boiler to a degree I wasn't comfortable with. The t87 did dip under the set point that I noticed but it never overshot, ever. I watched that with a few different thermometers
    You can have it good, fast or cheap. Pick two
  • Techman
    Techman Member Posts: 2,144
    edited February 2016
    The "room indicator" is adjustable. The heat anticipator,heats up the "spring" and turns the heat off slightly before the room gets up to temp by anticipating that the "residual" heat in the system will finish the job and bring the room temp up to room temp.
    I re-calibrate those "old" T'stats with that special wrench.
  • ChrisJ
    ChrisJ Member Posts: 16,316
    Canucker said:

    I haven't been able to equal the control my old t87 had for the basement zone. 2 cycles overshoots/undershoots by at least 1 degree celsius. I tried 3 and 4 cph but it ended up short cycling my boiler to a degree I wasn't comfortable with. The t87 did dip under the set point that I noticed but it never overshot, ever. I watched that with a few different thermometers

    How long did you run 3 or 4 CPH?
    The VP8000 slowly learns and tweaks it self but it days a while.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • JUGHNE
    JUGHNE Member Posts: 11,279
    Yep, agree with all that. But for the OP....no batteries..no concern about a "common" wire.....and they are "free" to him.
    Plus that word "comfortable" comes into play.
  • The benefit of a good digital is in the ability to raise the temp just one degree, if someone complains. That's harder to do with the old style.--NBC
  • Gordy
    Gordy Member Posts: 9,546
    Key word comfortable. That's a feeling not anobservation
  • Canucker
    Canucker Member Posts: 722
    ChrisJ said:

    Canucker said:

    I haven't been able to equal the control my old t87 had for the basement zone. 2 cycles overshoots/undershoots by at least 1 degree celsius. I tried 3 and 4 cph but it ended up short cycling my boiler to a degree I wasn't comfortable with. The t87 did dip under the set point that I noticed but it never overshot, ever. I watched that with a few different thermometers

    How long did you run 3 or 4 CPH?
    The VP8000 slowly learns and tweaks it self but it days a while.
    I only ran it for a couple of days. It's not a high end stat, do all the honeywells have a learning curve? I ask because the other 2 zones use a honeywell model that adjusts when it recovers from set back so you're at temp when you requested instead of starting at that time. The basement one doesn't and i've never adjusted their cph. (They overshoot too, especially when it's warmer out)
    You can have it good, fast or cheap. Pick two
  • ChrisJ
    ChrisJ Member Posts: 16,316
    Canucker said:

    ChrisJ said:

    Canucker said:

    I haven't been able to equal the control my old t87 had for the basement zone. 2 cycles overshoots/undershoots by at least 1 degree celsius. I tried 3 and 4 cph but it ended up short cycling my boiler to a degree I wasn't comfortable with. The t87 did dip under the set point that I noticed but it never overshot, ever. I watched that with a few different thermometers

    How long did you run 3 or 4 CPH?
    The VP8000 slowly learns and tweaks it self but it days a while.
    I only ran it for a couple of days. It's not a high end stat, do all the honeywells have a learning curve? I ask because the other 2 zones use a honeywell model that adjusts when it recovers from set back so you're at temp when you requested instead of starting at that time. The basement one doesn't and i've never adjusted their cph. (They overshoot too, especially when it's warmer out)
    Not sure.
    I know the VP8000 does but Honeywell doesn't say much about how their thermostats work which is annoying.

    For example, I still have no idea what the difference between a normal VP8000 is, and the commercial version that was a lot more money.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Canucker
    Canucker Member Posts: 722
    I noticed that about Honeywell, hard to find out what their features actually do. I checked my tstats and set them all to 4 cph from the 3 they were set at. I guess I'll watch them for a week and see what happens.
    You can have it good, fast or cheap. Pick two
  • fulljionslly
    fulljionslly Member Posts: 1
    I don't know how yours work.But I bought a multifunctional humidity meter few months ago,which with date, week, time, humidity, temperature, alarm clock, and back light. It also a perfect for travel, home and outdoor use, which is convenient to carry.I think it's worth buying one.If you want to change a new one,I recommend you this one.https://fulljion.com/large-display-digital-temperature-humidity-thermometer-home-comfort-monitor.htmlAnd the reason I choose digital one is that I can have lots of functions in this small humidity meter,it is really convenient~If you want to know more about my humidy meter, I can give you the official website~
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    edited July 2017
    @fulljionslly...booooooooo.
    You created an account name and posted once about a specific product? Hmmmm....I'm sure it will get bounced shortly. Or you could purchase an ad on this site.

    There was an error rendering this rich post.