Alan (California Radiant) Forbes
Member Posts: 4,011
I have a customer who wants a warmer room. He has wall-to-wall BB with some bare piping where the fins have been removed by the installer. Is there a product that can be snapped on to the copper without having to cut the copper to increase output?
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab
Two btu per sq ft for degree difference for a slab
0
Comments
-
I remember a similar discussion from years ago somewhere here on the wall. If memory serves me correctly, there is, or was a product that can be clipped over the pipe. Don't ask me who or what manufacturer because I don't recall.0
-
never used this but this might work: FabTek Logic
Element
Hydronic Baseboard
Fin Clamp
http://www.parksupplyofamerica.com/product.php?id=FCL-.5CX1FT&fam=P9MH3AIQK61N&addons=y0 -
Perfect - Thanks, Michael!8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0
Categories
- All Categories
- 85.7K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 49 Biomass
- 418 Carbon Monoxide Awareness
- 71 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 847 Plumbing
- 5.8K Radiant Heating
- 371 Solar
- 14.5K Strictly Steam
- 3.2K Thermostats and Controls
- 50 Water Quality
- 38 Industry Classes
- 47 Job Opportunities
- 15 Recall Announcements