Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Adding output to existing baseboard.
Alan (California Radiant) Forbes
Member Posts: 4,249
I have a customer who wants a warmer room. He has wall-to-wall BB with some bare piping where the fins have been removed by the installer. Is there a product that can be snapped on to the copper without having to cut the copper to increase output?
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab
Two btu per sq ft for degree difference for a slab
0
Comments
-
I remember a similar discussion from years ago somewhere here on the wall. If memory serves me correctly, there is, or was a product that can be clipped over the pipe. Don't ask me who or what manufacturer because I don't recall.0
-
never used this but this might work: FabTek Logic
Element
Hydronic Baseboard
Fin Clamp
http://www.parksupplyofamerica.com/product.php?id=FCL-.5CX1FT&fam=P9MH3AIQK61N&addons=y0 -
Perfect - Thanks, Michael!8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements