Want to get professional opinion. I want to replace the rusted and inadequate old vent but it is so badly rusted that it is very hard to get to; bushing is also rusted. Even if we were able to get it off, it is too close to the ceiling so is most likely picking up runoff and debris. The plumber who did the conversion from oil to gas did not replace this decades old vent. That section of the pipe is cold and we have cold radiator issue on top floor. So this has to be fixed as immediate next step. The location of this vent makes it very hard so looking for creative solution here. See attached diagram of current and proposed.
What I am thinking is that I have a vent installed not at the elbow but slightly below the bend. The final drop is a copper pipe so should not be too hard to tap/weld and put a Gorton #2 vent there.
Questions:
1- How high should the vent be above the water line?
2- Any other considerations for the vent in terms of some basic steam principles that I should keep in mind?
Thank you!

What I am thinking is that I have a vent installed not at the elbow but slightly below the bend. The final drop is a copper pipe so should not be too hard to tap/weld and put a Gorton #2 vent there.
Questions:
1- How high should the vent be above the water line?
2- Any other considerations for the vent in terms of some basic steam principles that I should keep in mind?
Thank you!

0
Leave a Comment
Categories
- 80.9K THE MAIN WALL
- 2.5K A-C, Heat Pumps & Refrigeration
- 36 Biomass
- 394 Carbon Monoxide Awareness
- 2.6K Controls
- 1.4K Domestic Hot Water
- 3.7K Gas Heating
- 100 Geothermal
- 130 Indoor-Air Quality
- 2.3K Oil Heating
- 30 Pipe Deterioration
- 563 Plumbing
- 4.2K Radiant Heating
- 333 Solar
- 12.1K Strictly Steam
- 36 Water Quality
- 7 Industry Classes
- 51 Job Opportunities
- 7 Recall Announcements
Comments
How long is that steam main, and what pipe size?
"Reducing our country's energy consumption, one system at a time"
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Baltimore, MD (USA) and consulting anywhere.
https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc
If your only option is to mount the vent on the vertical drop, then it must be as high as possible above the waterline. The water level in the returns rises 1.75 inches per ounce of pressure above the waterline of the boiler. This rising return water level can block the vent connection if it is not high enough.--NBC
New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com
"Reducing our country's energy consumption, one system at a time"
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Baltimore, MD (USA) and consulting anywhere.
https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc
What is shocking is that the return currently has a very tiny valve, which is corroded and rusty and none of the plumbers who came diagnosed that cold pipe to be the issue, so i had to do the research and i hope i am on the right track...
"Reducing our country's energy consumption, one system at a time"
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Baltimore, MD (USA) and consulting anywhere.
https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc
Home is Two floors, 3 bedroom per floor residential - two Gorton #2s?! Ok, I'm on it... since the return pipe at the end if 1" there may be diminishing returns beyond 2 vents too...