Head Loss through the MPO-IQ

Harvey Ramer
Member Posts: 2,264
Anyone know off hand where to find the head loss through the Burnham MPO-IQ. Can't find it in the manual. Particularly interested in the 189.
0
Comments
-
Not much. I think Burnham seems to be more concerned about a 20 degree delta T between supply/return.
Are you in the design phase of something?There was an error rendering this rich post.
0 -
Trouble shooting. The only real loss would be from the return injection tube where it necks down to 3/4" pipe for 4 or 5 inches. I got in contact with US boiler today and while they don't have any published data on it, they said it is a small pressure drop.0