high vacuum advice tiger loop 2 stage pump
captainjdog
Member Posts: 2
in Oil Heating
Been troubleshooting a boiler for a few months, but i think I finally have it narrowed down. The pump is 11 feet above the tank and a run of about 20 feet. Its a 2 pipe system with a single stage suntec pump. Just ran new 3/8s lines & new filters (2 inline). Its currently pulling 13 in. hg vacuum. The system fails at 18 in hg which takes about a month. It doesnt take long and I'm always nervous I will come home to a frozen house.
I can't figure out a way to lower the vacuum any more so I ordered a 2 stage pump because 13.in hg - 18 in. hg is too high for the single stage. Apparently 2 stage is good for 17 in hg. vacuum.
Do you think this system is a prime candidate for a tiger loop?
Or would a booster pump work better?
I have zero experience with either.
My goal is to reduce the required maintence on the system and improve reliability. My thoughts are a tiger loop would extend filter service and reduce vacuum on the pump. Im not sure if anyone can chime in on the reduced vacuum using a tiger loop. I would think I still can't get around the 11in hg required to lift the oil 11 feet.
Any advice before I head down this road?
Thanks
I can't figure out a way to lower the vacuum any more so I ordered a 2 stage pump because 13.in hg - 18 in. hg is too high for the single stage. Apparently 2 stage is good for 17 in hg. vacuum.
Do you think this system is a prime candidate for a tiger loop?
Or would a booster pump work better?
I have zero experience with either.
My goal is to reduce the required maintence on the system and improve reliability. My thoughts are a tiger loop would extend filter service and reduce vacuum on the pump. Im not sure if anyone can chime in on the reduced vacuum using a tiger loop. I would think I still can't get around the 11in hg required to lift the oil 11 feet.
Any advice before I head down this road?
Thanks
0
Comments
-
Webster Service Tech Handbook.
Relevant information starts around page six.
http://www.websterfuelpumps.com/pump_docs/LL4640.pdf
Seems to indicate a 2 stage would be better. Possibly larger oil line also.0 -
This is a perfect candidate for the Loop, I've done overhead shop furnaces with this exact scenario with total success. I would do either the Tiger Ultra with integral spin on filter and hg gauge or 1 spin on filter at tank. The extra filter adds unnecessary restriction- something you don't need. I would put on the 2 stage pump, 3/8" ID line would be better if doable, otherwise see how it pulls with the 1/4".
I've got systems running like this for almost 25 years.0 -
Thanks for the response Bob, and for the information 776v63.
I'll post my successful results0 -
Tigerloop is the way to go by only pulling 1 pipe you will only pull the firing rate of furnace through the line which will drop the vaccum .0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements