LWCO Malfunctioning? (Video Included)
I decided to test the LCWO, I drained the water to simulate a low water condition and shot the video below...
https://www.youtube.com/watch?v=jsymZet_YGU
I have two issues really: whats causing the LCWO to not sense correctly, and is it operating correctly when it does?
Comments
-
Any thoughts?0
-
If you drain some more water does it work? Either it's not wired right to feed water, it's not working, or there's a delay to wait for the condensate to return.
The LWCO should shut the burner off. If the water level drops and it doesn't do that (assuming it's wired right) it needs to be replaced.
That boiler needs to be skimmed.
Is this a new problem?
I do see the light go out in the LWCO, when that happens, is any power going to the water feeder? I also noticed a valve closed, but that appears to be a fast fill valve.
If you ok with electric, I would first go thru and start checking, tugging on wire nuts. Then start checking the sequence of operations with my meter.
If you're not ok, I would have a tech do it.There was an error rendering this rich post.
0 -
fill water up manually and see if boiler comes on.0
-
If you can't solve this easily, call a pro. A LWCO that doesn't work can let the boiler fire with no water in it, which will crack the cast-iron and you'll need a new boiler.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
If I had any question as to my LWCOs ability to do it's job I'd replace it immediately.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Have you taken the LWCO probe out and cleaned it with some fine steel wool? Maybe even replace the probe. Don't use teflon tape tape on it when you put it back as it needs to ground to the boiler block. It may need to be replaced. With it switching on and off like that, it probably isn't allowing enough time for the water feeder to activate.0
-
Sigh,Fred said:Have you taken the LWCO probe out and cleaned it with some fine steel wool? Maybe even replace the probe. Don't use teflon tape tape on it when you put it back as it needs to ground to the boiler block. It may need to be replaced. With it switching on and off like that, it probably isn't allowing enough time for the water feeder to activate.
Fred, you have to use thread sealant on the probe, its NPT.
3 wraps of PTFE tape, or some pipe dope are required or it will leak.
The warnings are not to go crazy with PTFE tape or it may not ground good to the block.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
I would use pipe dope but PTFE is a hit or miss, IMHO.ChrisJ said:
Sigh,Fred said:Have you taken the LWCO probe out and cleaned it with some fine steel wool? Maybe even replace the probe. Don't use teflon tape tape on it when you put it back as it needs to ground to the boiler block. It may need to be replaced. With it switching on and off like that, it probably isn't allowing enough time for the water feeder to activate.
Fred, you have to use thread sealant on the probe, its NPT.
3 wraps of PTFE tape, or some pipe dope are required or it will leak.
The warnings are not to go crazy with PTFE tape or it may not ground good to the block.
EDIT: My thinking here is that the OP may be having a problem with a probe that just may not be grounding so avoid the tape as a means of eliminating that possibility. I know some use tape with no problem. Most suggest dope anyway.0 -
How many probes have you installed using PTFE and how many had problems?Fred said:
I would use pipe dope but even PTFE is a hit or miss, IMHO.ChrisJ said:
Sigh,Fred said:Have you taken the LWCO probe out and cleaned it with some fine steel wool? Maybe even replace the probe. Don't use teflon tape tape on it when you put it back as it needs to ground to the boiler block. It may need to be replaced. With it switching on and off like that, it probably isn't allowing enough time for the water feeder to activate.
Fred, you have to use thread sealant on the probe, its NPT.
3 wraps of PTFE tape, or some pipe dope are required or it will leak.
The warnings are not to go crazy with PTFE tape or it may not ground good to the block.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Exactly how many have you installed besides the one on your boiler? See my Edit note on my prior post.0
-
I'm not the one saying PTFE causes problems.Fred said:Exactly how many have you installed besides the one on your boiler? See my Edit note on my prior post.
I see your note, and agree with it, except that I doubt 3 wraps of quality tape will cause any issue.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
I'm not the one saying it won't cause a problem.ChrisJ said:
I'm not the one saying PTFE causes problems.Fred said:Exactly how many have you installed besides the one on your boiler? See my Edit note on my prior post.
I see your note, and agree with it, except that I doubt 3 wraps of quality tape will cause any issue.
Just trying to help the OP.0 -
Thanks for the comments everyone, I just went ahead and ordered a new LWCO. The problems just seem to be staking up with this one. For a while now it's been short-cycling the burner when in a low water scenario. Maybe it's just a malfunctioning probe, but it's a small price to pay for piece-of-mind.
The water feeder is set on LWCO and 6min delay. In my mind, there is no reason why the LWCO yellow light should be turning off until the water level is raised to an appropriate level by the feeder. The noise in the video is the relay in the LWCO, it just seems to be malfunctioning...0 -
I replaced the LWCO with a new one, and all is working perfectly!
I see why it's not a bad idea to have a backup LWCO...0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements