Old 7" Baseray ratings

cchuc
cchuc Member Posts: 3
Does anyone have the output ratings of the old 7" baseray system? I can find the tables for the 9A but haven't been able to find it for the 7. If no tables does anyone have a multiplier they use to adjust from the 9A tables?
thanks for any help
Chris

Comments

  • Tinman
    Tinman Member Posts: 2,808
    Here ya go.
    Steve Minnich
    Bob Bona_4STEVEusaPA
  • Bob Bona_4
    Bob Bona_4 Member Posts: 2,083
    Had the same question a few months ago :)
  • cchuc
    cchuc Member Posts: 3
    Thanks for the quick reply Stephen
    They show the SF/lin ft, is that the same as the steam rating (in SF) I see on the 9A table? If I compare 2.08 to the 9A ratings of 3.4 I get a ratio that the old 7" is 0.6 the rating of the 9A. My system is hot water, can I just multiply the BTU/Hr ratings in the 9A hot water table by that same ratio? Or is there something different about the steam rating that it can't be applied to the hot water ratings?
    Thanks again
    CHris
  • bob_46
    bob_46 Member Posts: 813
    Try this

    There was an error rendering this rich post.

    Tinman
  • Rich_49
    Rich_49 Member Posts: 2,769
    Must be a run on buildings that have 7A in them . Just got this one from Burnham this morning .
    You didn't get what you didn't pay for and it will never be what you thought it would .
    Langans Plumbing & Heating LLC
    732-751-1560
    Serving most of New Jersey, Eastern Pa .
    Consultation, Design & Installation anywhere
    Rich McGrath 732-581-3833
  • Rich_49
    Rich_49 Member Posts: 2,769
    And another just in from Burnham
    You didn't get what you didn't pay for and it will never be what you thought it would .
    Langans Plumbing & Heating LLC
    732-751-1560
    Serving most of New Jersey, Eastern Pa .
    Consultation, Design & Installation anywhere
    Rich McGrath 732-581-3833
  • Rich_49
    Rich_49 Member Posts: 2,769
    Here it is
    You didn't get what you didn't pay for and it will never be what you thought it would .
    Langans Plumbing & Heating LLC
    732-751-1560
    Serving most of New Jersey, Eastern Pa .
    Consultation, Design & Installation anywhere
    Rich McGrath 732-581-3833
    Tinman
  • cchuc
    cchuc Member Posts: 3
    thanks Bob and Rich. I appreciate all the help
  • MrCofDG
    MrCofDG Member Posts: 40
    Hi Gents, anyone know what the water capacity (gallon/foot) is of 7" Base-Ray ? The 9 7/8” tall Base-Ray is 0.3 gal/foot, per the Installation Manual.
  • MrCofDG
    MrCofDG Member Posts: 40
    My estimate of Volume of Water per Foot for 7" Base-Ray:
    given the 1" diameter of each internal pipe (or horizontal 'cylinder'; I measured it 5/22/2020), then the volume of a 1-foot 'cylinder' = Pi X r x r x height (or length in this case!) => 3.1416 x 0.5" x 0.5" x 12" = 9.4248 cubic inches = 0.04 gallon in each 'cylinder', so given 2 'cylinders' in each foot of Base-Ray =>0.08 gallon per foot of Base-Ray.