Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
EDR calculation for old existing boiler, way oversized??
SteamingPile
Member Posts: 14
I used this link to figure out the numbers for my existing system:
http://www.smithfieldsupply.com/company_info/forms/radiatorest.pdf
Something seems off...
11 radiators of varying types:
40 sq ft hallway
50 sq ft big kitchen
34 sq ft small sitting room
34 sq ft kid bedroom 1
37 sq ft kid bedroom 2
27 sq ft 2nd floor full bath
34 sq ft upstairs office
16 sq ft small 1/2 bath
24 sq ft living room A
24 sq ft living room B
34 sq ft small 1st floor bed
... This totals around 354 sq ft.
*1.25 factor= ~442 sq ft (under the impression that the extra 25% is allowance for piping loss, etc)
My existing american standard is 713 sq ft (~45+ year old).... I've found one floor hole in the kitchen where there was probably a radiator but that's it, even a large one would add another 50 sq ft.
Did they size boilers huge back in the day? When this sucker runs it eats oil.
I'm starting to do research on boiler replacement for when oil starts to creep up in price. Got the wood stove cranking so I can keep the heat up to a comfortable level during the day.
http://www.smithfieldsupply.com/company_info/forms/radiatorest.pdf
Something seems off...
11 radiators of varying types:
40 sq ft hallway
50 sq ft big kitchen
34 sq ft small sitting room
34 sq ft kid bedroom 1
37 sq ft kid bedroom 2
27 sq ft 2nd floor full bath
34 sq ft upstairs office
16 sq ft small 1/2 bath
24 sq ft living room A
24 sq ft living room B
34 sq ft small 1st floor bed
... This totals around 354 sq ft.
*1.25 factor= ~442 sq ft (under the impression that the extra 25% is allowance for piping loss, etc)
My existing american standard is 713 sq ft (~45+ year old).... I've found one floor hole in the kitchen where there was probably a radiator but that's it, even a large one would add another 50 sq ft.
Did they size boilers huge back in the day? When this sucker runs it eats oil.
I'm starting to do research on boiler replacement for when oil starts to creep up in price. Got the wood stove cranking so I can keep the heat up to a comfortable level during the day.
0
Comments
-
You don't need to add the 1.25 factor. It's already included in the rating of the boiler. If your calculatation are correct you need a boiler around 354 sq.ft. steam. Your boiler is 100% oversized.
The best thing you can do is check for air infiltration around doors/windows/etc to reduce fuel consumption. After that consider improving your insulation.0 -
That boiler was probably installed when oil was less than 15 cents a gallon (That's what it was in 1970 when I got out of the army). There were two sizes to choose from - too big and much too big.
I agree the best thing you can do is find and eliminate any air infiltration; then beef up the insulation. When the time comes find someone who understands steam and put in a properly piped Megasteam.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge1 -
Thanks guys.Abracadabra said:You don't need to add the 1.25 factor. It's already included in the rating of the boiler. If your calculatation are correct you need a boiler around 354 sq.ft. steam. Your boiler is 100% oversized.
The best thing you can do is check for air infiltration around doors/windows/etc to reduce fuel consumption. After that consider improving your insulation.
Wow 100% oversized. That's insane. Not only that but it's my only hot water source so its burning oil constantly.
I'm not sure how to find out the year since American Standard sold off their division I guess right around 1970 (?). I figure its ~1970
at the latest.
This house is older, 1880-ish but does have some fiberglass wall insulation from when the previous-previous owners did drywall.
It's new to me so I'm not sure if its throughout.
Every window in the place was replaced with double pane low E vinyl so at least the windows are sealed well. I've been hunting drafts for a week now and have got most of them I think.
0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements