  • CMadatMe
    CMadatMe Member Posts: 3,086
    There's the pressure drop across the HX, you tell me the right speed? It's 3....

    There was an error rendering this rich post.

  • sunlight33
    sunlight33 Member Posts: 378
    Isn't that assuming the boiler is working 100% at 114,000 Bth/h? What if the boiler is only working at 40% of that?
  • GW
    GW Member Posts: 4,832
    The flow is a constant, it's a fixed speed pump. It's kinda confusing if you let it be. The boiler is looking to make a certain temp. So if you're at 40%, your boiler is seeing 40% of its total capacity for a load. Get it, or no?

    So, if you're plugging along at 40%, let's pretend you open all your windows for some nice fresh air. Your heat flys out and cold flys in, dropping to the floor. Your heat emitters will now shed its BTU's faster right? Now the boiler will Rev up becasue the return temps are lower.

    So, lower return temp means a larger hill to climb, the boiler will start working harder.
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
    CMadatMe
  • sunlight33
    sunlight33 Member Posts: 378
    Thank you Chris and GW for the clarification.
    CMadatMe
  • sunlight33
    sunlight33 Member Posts: 378
    Is it true that mod-con running on propane can condense roughly 10 degrees higher than running on nat gas?
  • CMadatMe
    CMadatMe Member Posts: 3,086
    Condensing is all about the dew point, ie CO2...

    There was an error rendering this rich post.

  • sunlight33
    sunlight33 Member Posts: 378
    I see, take 10% CO2 from propane vs. 8.5% from methane. That's like 131F vs. 123F according to the graph.
  • sunlight33
    sunlight33 Member Posts: 378
    Last night the temperature got as low as -9F, and the boiler still cycled on/off about 1.5 to 2 times an hour (very similar to when the temperature was in the 20's), any thoughts on that? I am curious as to why the boiler wouldn't just modulate lower and burn at a longer interval.
  • CMadatMe
    CMadatMe Member Posts: 3,086
    edited February 2016
    The bottom end of the modulation rate is what it is and if the system side isn't putting demand on the boiler then why would it go into higher fire? Two cycles in an hour at -9 for seems really good. Boiler wants to coast not peddle to the metal. I noticed you didn't say the house was cold. :)

    There was an error rendering this rich post.