Pressuretrols and Trapped pressure

2»

Comments

  • Major7
    Major7 Member Posts: 44
    One is private label for the other. Same boiler.
  • Major7
    Major7 Member Posts: 44
    Or maybe not... Will have to look into.
  • Steamhead
    Steamhead Member Posts: 17,183
    Major7 said:

    Or maybe not... Will have to look into.

    Definitely not.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Major7
    Major7 Member Posts: 44
    My bad. For some reason, the documentation and the warranty that came with the house were from Weil McClain, but the boiler is most def a Utica. Could be the WM was the prior boiler.
  • Steamhead
    Steamhead Member Posts: 17,183
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • LarryK
    LarryK Member Posts: 46
    Or look here and avoid the ads. I have the same boiler.
    http://www.uticaboilers.com/documents/archived
    Look under PEG-E. You also need the wiring addendum.
  • Major7
    Major7 Member Posts: 44
    Problem is resolved. Pigtail was so clogged that pipe cleaners could not get through to clean it out. I called in a local steam heat specialist, and they managed to break off the pigtail at the thread joint when taking it off. There is so much gunk in the pigtail outlet that the boiler will still run without spewing out steam. It's the weekend now, but they will install a new pigtail, repipe the fresh water feed, and replace two mains vents on Monday.

    Thanks for all your help!
  • New England SteamWorks
    New England SteamWorks Member Posts: 1,521
    Replace main vents with what? Very important detail here that will, in all likelihood, drastically cut down on cycle run time. Right now your boiler just runs and runs trying to chase the air out of the mains before the steam can even get to where it needs to go. It they put the type of vents that are usually used it won't be much of an improvement.

    Time for a Big Mouth intervention, me thinks.
    New England SteamWorks
    Service, Installation, & Restoration of Steam Heating Systems
    newenglandsteamworks.com
  • Major7
    Major7 Member Posts: 44
    Excellent question. The mains are nearly at the ceiling line, and there is only room for a small vent. They are Hoffman 4As, and they are completely closed off. I purchased two Gorton #2s last year, but they are absolutely huge. I don't see how to fit them in the space I have available.
  • Fred
    Fred Member Posts: 8,542
    The Barnes and Jones Big Mouth vents are smaller than the Gorton #2's and each Big Mouth has the capacity of better than 2 of the Gorton's. Consider them:
    https://www.amazon.com/Barnes-Jones-Big-Mouth-Vent/dp/B01F26P13C/ref=sr_1_1?ie=UTF8&qid=1475956220&sr=8-1&keywords=Barnes+and+Jones+Big+Mouth+vent

    Also, The Barnes and Jones Varivent is much smaller and they are about equal to a Gorton #2 in capacity
    https://www.amazon.com/Barnes-Jones-BJ-2VV-NPT-Vari-Vent/dp/B01GQP0DQ8/ref=sr_1_1?ie=UTF8&qid=1475956335&sr=8-1&keywords=Barnes+and+Jones+Varivent
  • Steamhead
    Steamhead Member Posts: 17,183
    Major7 said:

    Excellent question. The mains are nearly at the ceiling line, and there is only room for a small vent. They are Hoffman 4As, and they are completely closed off. I purchased two Gorton #2s last year, but they are absolutely huge. I don't see how to fit them in the space I have available.

    Take a pic and post it here.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Major7
    Major7 Member Posts: 44
    https://goo.gl/photos/qt9Ju27RFVZp6fJT7

    Hope this works. These are from last year. I since cut away some of the drywall, and found that there is an adjacent joist on both main vents.
  • Major7
    Major7 Member Posts: 44
    Is there a site where I can get better details on the external dimensions of the B&J products? Their public website seems to be geared towards steam traps.
  • BobC
    BobC Member Posts: 5,489
    The big mouth has a 3/4" diameter tail piece you screw into the pipe and then the vent mounts to that with a union fitting. You need about 4-1/2" height above the fitting your mounting it to.

    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • Major7
    Major7 Member Posts: 44
    Thanks. My biggest problem with the vent is its diameter. I uploaded a photo into the same folder that shows the vent basically touches the joist. Anything that sticks out would prevent the installer from spinning it onto the nipple.
  • Fred
    Fred Member Posts: 8,542
    Major7 said:

    Thanks. My biggest problem with the vent is its diameter. I uploaded a photo into the same folder that shows the vent basically touches the joist. Anything that sticks out would prevent the installer from spinning it onto the nipple.

    It doesn't have to be spun onto the nipple. You take the tail piece off of the vent, screw it into a female fitting on the nipple and then mount the vent using the union type connection on the vent. Vent doesn't spin, just the union fitting.
  • KC_Jones
    KC_Jones Member Posts: 5,756
    Fred said:



    Vent doesn't spin, just the union fitting.

    Another advantage of the Big Mouth.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • BobC
    BobC Member Posts: 5,489
    You will need a 5/8" hex key to tighten the tailpiece, then you sit the bigmouth on top of the tailpiece and tighten the union nut.

    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge