I had a service call at a large apartment building today for no heat. Both pumps were missing their start capacitors and nobody knew where they went.
I called around and apparently there isn't even a part number for the caps? No chance that anyone knew the specs of the caps. They're saying the complete motor and/or pump must be replaced? Does anyone have any information on Series 60 start capacitors?
I took a somewhat educated, WAG as to the cap size and did a 2 second run on each pump and they worked. I did that only to verify that there's a decent chance the pump and bearing assembly are good.
Anyone?
I had a service call at a large apartment building today for no heat. Both pumps were missing their start capacitors and nobody knew where they went.
I called around and apparently there isn't even a part number for the caps? No chance that anyone knew the specs of the caps. They're saying the complete motor and/or pump must be replaced? Does anyone have any information on Series 60 start capacitors?
I took a somewhat educated, WAG as to the cap size and did a 2 second run on each pump and they worked. I did that only to verify that there's a decent chance the pump and bearing assembly are good.
Anyone?
Steve Minnich
0
Comments
-
-
3/4 hp, dual voltage motor wired to 115Steve Minnich0
-
Most start caps are taken out of the circuit by a potential relay, this one taken out by a centrifugal switch although that shouldn't matter. The maintenance men said they had no idea what happened to the capacitors. Really? My guess is someone robbed Peter to pay Paul.Steve Minnich0
-
-
Joe - I appreciate the help. I did call the local rep. They said no part number and no specs. I will follow up based on what you shared. If you have a parts list that includes the capacitor, please email it to me. Thanks again.Steve Minnich0
-
Here in the DC area we have a Co. called Southern Utilities and I bet they know.0
-
Stephen, looked thru some of my stuff and found a parts list for the series 60 b&g it shows the start cap part number Joe mentioned.
1 -
I have 2 series 60's in use they are 120 vac 1/2 HP though. I can look tomorrow what start cap they use. As long as it starts and the centrifugal switch disconnects it from the windings. It is only in use for less than a second. If it stays energized sometimes they explode, ( Just ask how I know).1
-
Call a shop that rewinds motors. They will be able to tell you.0
-
@Joe and Abracadabra - I forwarded that part# to my guy at my supply house last night and he's thinking that it's still a valid number. And, it is a run capacitor on that motor. The last few Series 60's (617S) I worked on used start caps. This one is actually a PSC motor.
A huge thanks for the assist.Steve Minnich0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements