Supply size for shower heads body sprays 10 gpm ?
Comments
-
replace both with 3/4 if you can. You only talking 20 feet. This table gives you an idea of flow rates. Ideally you want to be around 4 fps, but for an intermittent load PHCC tables allow up to 8fps.
There may be times when you are flowing 100% hot as the water heater drains down.
Got enough water heater to keep up with that demand?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Hot Rod, thank you for the input. I can't change them to 3/4 would have to rip out kitchen. I found a way to pick up the 1/2 from the sink faucets that are in the bath room, and join them to the shower. Two 1/2 pipes from different feeds in the house. Any problems except longer to wait for hot water. I wonder if they will act as gravity hot water Re-circulation some what. I love your heated shower ideas in previous posts and incorporating them into this bath remodel. I used one zone for the floor and shower walls all together, what do you normally do. Can you send some pictures of you shower wall radiant piping. Thanks again.0
-
"Got enough water heater to keep up with that demand"?
Maybe that went un-noticed. It's very important. Clock the flow, because you can do anything you want , but if you can't get it from the street, you're done.0 -
Sounds like a manifold approach? Sure multiple lines would increase available flow, as long as the other end of those sink runs connects to a 3/4 line?heathead said:Hot Rod, thank you for the input. I can't change them to 3/4 would have to rip out kitchen. I found a way to pick up the 1/2 from the sink faucets that are in the bath room, and join them to the shower. Two 1/2 pipes from different feeds in the house. Any problems except longer to wait for hot water. I wonder if they will act as gravity hot water Re-circulation some what. I love your heated shower ideas in previous posts and incorporating them into this bath remodel. I used one zone for the floor and shower walls all together, what do you normally do. Can you send some pictures of you shower wall radiant piping. Thanks again.
Any way to snake 3/4 pex across the kitchen, add that to the 1/2 at the shower?
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Hello: How about smallifying the problem and using 1.5 gpm showerheads? Niagra makes some good ones. Reducing flow by 40% couldn't hurt, plumbing-wise.
Yours, Larry0 -
The little calc wheel? It came as part of our membership in the PHCC many years ago. It must be 25 plus years old.Hilly said:@Hotrod where did you find that nice little tool?
I'd guess there are electronic versions in this day and age, like the System Syzer wheel?
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Larry, in my experience, people that are interested in having a mega car-wash style shower with his/hers shower heads, rain heads, body sprays, etc. are not going to be worried about 1.5gpm spray heads, nor would they want them.Larry Weingarten said:Hello: How about smallifying the problem and using 1.5 gpm showerheads? Niagra makes some good ones. Reducing flow by 40% couldn't hurt, plumbing-wise.
Yours, Larry0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements