Can't get 100% water to drain from return outlet.

Yet again, I am desperate. Someone else wrote that they drained their boiler from the return valve, then refilled it and they haven't had any noise since then. I can only get about 64oz out of my boiler at that level. Why so little?

Comments

  • Mark N
    Mark N Member Posts: 1,115
    From the return you can only drain down to the level of the Hartford loop.
  • BobC
    BobC Member Posts: 5,495
    You want to drain from the white handled valve in the 3rd picture, that is the boiler drain. The one with the hose on it is the return drain it will not drain the boiler completely.

    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • heatseeker1
    heatseeker1 Member Posts: 72
    Thanks so much for clearing that up..