Mod-Con Boiler and system questions???

13»

Comments

  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,601
    For everyone's consideration. Often overlooked.
    Retired and loving it.
  • Rich_49
    Rich_49 Member Posts: 2,769
    If the boiler does not see those low return temps it's all for nothing
    You didn't get what you didn't pay for and it will never be what you thought it would .
    Langans Plumbing & Heating LLC
    732-751-1560
    Serving most of New Jersey, Eastern Pa .
    Consultation, Design & Installation anywhere
    Rich McGrath 732-581-3833
    Gordy
  • njtommy
    njtommy Member Posts: 1,105
    @Paul48 the Ahu you see has the same water running through coil as your faucets.
    I would assume the coil is designed for a 40 degree delta t
  • Paul48
    Paul48 Member Posts: 4,469
    Define your system as well as Chester did, and we could answer that question.
  • Paul48
    Paul48 Member Posts: 4,469
    njtommy...........That scenario is un-desirable as far as I'm concerned.
  • njtommy
    njtommy Member Posts: 1,105
    Why's that @Paul48?
  • Brewbeer
    Brewbeer Member Posts: 616
    @Paul48 - SWT 114F, return temp 109F, boiler fire rate 20%.
    Hydronics inspired homeowner with self-designed high efficiency low temperature baseboard system and professionally installed mod-con boiler with indirect DHW. My system design thread: http://forum.heatinghelp.com/discussion/154385
    System Photo: https://us.v-cdn.net/5021738/uploads/FileUpload/79/451e1f19a1e5b345e0951fbe1ff6ca.jpg
  • Gordy
    Gordy Member Posts: 9,546
    Brewbeer said:

    Along the lines of efficiency, I'd like echo one of Chester's comments a few posts up:



    "Do I really care what my [boiler] Delta T is if I have low return temps and long run times?"

    The boiler efficiency is where one of the biggest potential savings are. Along with less hardware to make that happen. Like @Rich said........

  • Paul48
    Paul48 Member Posts: 4,469
    Mixing heating and DHW?
  • Brewbeer
    Brewbeer Member Posts: 616
    Just heat.
    Hydronics inspired homeowner with self-designed high efficiency low temperature baseboard system and professionally installed mod-con boiler with indirect DHW. My system design thread: http://forum.heatinghelp.com/discussion/154385
    System Photo: https://us.v-cdn.net/5021738/uploads/FileUpload/79/451e1f19a1e5b345e0951fbe1ff6ca.jpg
  • Gordy
    Gordy Member Posts: 9,546

    For everyone's consideration. Often overlooked.

    That will be an interesting formula.

  • Rich_49
    Rich_49 Member Posts: 2,769
    @Paul48 . Don't really need a FPHX for hydro air , you can exercise the pump for 3 minutes a day to prevent contamination issues . Versa Hydro stores at up to 160* and WILL provide 160* temps if you need them , remember the sensor location is critical , the water above will be hotter than at that location . VS pump for tank / FPHX senses supply and return temps based on the programmed odr , return water is put back to the bottom of the tank .
    You didn't get what you didn't pay for and it will never be what you thought it would .
    Langans Plumbing & Heating LLC
    732-751-1560
    Serving most of New Jersey, Eastern Pa .
    Consultation, Design & Installation anywhere
    Rich McGrath 732-581-3833
  • Paul48
    Paul48 Member Posts: 4,469
    Provided you can get the necessary heat at somewhat closer to design temp, you don't have to worry about DT. With a low mass, fin-tube system, the buffer tank will delay the inevitable once we get into the arctic conditions.
  • Rich_49
    Rich_49 Member Posts: 2,769
    @Dan Holohan Too often forgotten . The HOUSE as a SYSTEM . Firing on all cylinders is BEST .
    You didn't get what you didn't pay for and it will never be what you thought it would .
    Langans Plumbing & Heating LLC
    732-751-1560
    Serving most of New Jersey, Eastern Pa .
    Consultation, Design & Installation anywhere
    Rich McGrath 732-581-3833
  • hot_rod
    hot_rod Member Posts: 23,422
    Gordy said:

    The spirit of the discussions is overall system efficiency, there are many micro, and macro efficiencies in a system that all come together to produce the big picture. Boiler,pumping,heat transfer,emitter,envelope to name a few. What efficiencies can take a hit to make others shine . System cost to achieve that goal, and create an exceptable ROI while providing ultimate comfort at cheap operating costs.

    That sums it up nicely.

    The challenge is for installers, designers and customers to wade through all the choices and options. Where to go to get accurate non-biased info to make comparisons.

    Remembering back 20- 30 years the first "perfect" radiant boiler was presented to us as the copper tube design. Basically a swimming pool heater morphed into a hydronic boiler.

    Manufacturers and reps promoted them as long lasting, a solid track record in pool use. Able to handle low return temperatures all day, excellent heat transfer material copper (that one is true) but in reality they were not so ideal. So they added staging gas valves to try and minimize short cycling and over-shooting temperatures. Then bypass piping was built in with a manual valve to adjust return, to help keep them from condensing to death. Then a pump was added to help blend return temperature. Then electronic controls.

    One of the big copper tube manufacturers told me "they would never build a mod con, no need the copper tube will do everything better" Never say never!

    Next were the coiled tube type mod cons, with about the same exact story. But they did in fact bring modulating, and a microprocessor to the table, and that was worth some of the pain and price the early adopters paid.

    Then the tank guys got into the picture, Polaris, HydroPulse, Voyager, and a few others. Those too were presented as the "perfect" hydronic boiler.

    Now on to mid mass. What exactly is the definition of mid-mass? Over 5 gallon, or more than 200 lbs of "mass" When does mid-mass turn into high mass? At 50 gallon or more fluid capacity?

    Regardless, every one of these has pros and cons, chose accordingly.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Paul48
    Paul48 Member Posts: 4,469
    Don't really need a FPHX for hydro air , you can exercise the pump for 3 minutes a day to prevent contamination issues .


    That validates the beliefs of every backwoods installation ever done. All I gots to do, is excersize my pump. And I didn't even know it was possessed.
  • Rich_49
    Rich_49 Member Posts: 2,769
    You may be onto something . Did you know the firetube heat exchanger was originally developed as a condensing component by moonshiners in WV? More liquor quicker !
    You didn't get what you didn't pay for and it will never be what you thought it would .
    Langans Plumbing & Heating LLC
    732-751-1560
    Serving most of New Jersey, Eastern Pa .
    Consultation, Design & Installation anywhere
    Rich McGrath 732-581-3833
  • Paul48
    Paul48 Member Posts: 4,469
    They had to catch them early in the day, to explain its construction. With all the sampling , by the end of the day, you'd never understand them.
    Rich_49
  • vicbrick
    vicbrick Member Posts: 20
    Appreciate all the thoughts/input on the various factors that impact hydronic heating efficiencies....Good Stuff!

    Ziggy presents a graph of Modcon boiler efficiency vs inlet/return water temperature at two different burner firing rates (25% and 100%). see attached pix. While the need to keep return water below ~125F to gain condensing efficiencies is often discussed, the efficiency differences at the 25% firing rate vs 100% firing rate with sub 100F return water is quite large. From the graph, the boiler efficiency drops by~ 5%, so 1/2 of the efficiencies of modcon is lost over a CI boiler when operating at 100% ouput ?

    Couple of questions:

    1) is the graph correct? Is it valid for both the TT style "firetube" heat exchanges and the spiral "honeycomb" style?
    2) If the graph is correct, how can most modcon boilers be rated as 95% efficient, when even under the most favorable conditions, they are operating around 90% efficient at full fire?
    Maybe the efficiency ratings are determined at 50% output?...a weighed average?






  • Chester
    Chester Member Posts: 83
    edited November 2015
    As I recall the video webinar posted above describes the laboratory conditions used to measure AFUE. The test doesn't seem to be based on anything resembling real-world conditions as much as it is a way to measure one unit against another based on some standard criteria. It was pretty revealing, especially the part about how the relatively high humidity required for the test creates "free" condensate that wouldn't necessarily be there with dry winter air. I think I recall they way they measure efficiency is simply by measuring the amount of condensate the unit spits out based on a given level of fuel burn.

    This certainly reinforces Hatterasguy's ongoing comments about how unfortunate it is that consumers buy (or are sold) "95% efficient" boilers just because that's what the AFUE sticker says, without regard to return water temps, etc. That's not to say that modcons can't be 95% efficient in a proper design, though.

    Gordy
  • Rich_49
    Rich_49 Member Posts: 2,769
    That Hatterasguy is perty darned smaht . LMAO
    You didn't get what you didn't pay for and it will never be what you thought it would .
    Langans Plumbing & Heating LLC
    732-751-1560
    Serving most of New Jersey, Eastern Pa .
    Consultation, Design & Installation anywhere
    Rich McGrath 732-581-3833
    HatterasguyCanucker
  • Paul48
    Paul48 Member Posts: 4,469
    Better question....what's Chester's background? Contractor? Homeowner? Either way, you're among the few that have a clue about mod/cons.
    Hatterasguy
  • Gordy
    Gordy Member Posts: 9,546
    Copy that!
    Hatterasguy
  • Rich_49
    Rich_49 Member Posts: 2,769
    Sound alot like Chester Birchwood . Is it ?
    You didn't get what you didn't pay for and it will never be what you thought it would .
    Langans Plumbing & Heating LLC
    732-751-1560
    Serving most of New Jersey, Eastern Pa .
    Consultation, Design & Installation anywhere
    Rich McGrath 732-581-3833
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,601
    You're contributing a lot, Chester. We need to hear stories like yours. Thanks for taking the time to tell it.
    Retired and loving it.
  • Paul48
    Paul48 Member Posts: 4,469
    Chester........Some of the finest heating contractors in the country come here. None of them were born with innate knowledge of heating systems (maybe 1 or 2). You are to be commended for what you have been able to teach yourself.
  • Gordy
    Gordy Member Posts: 9,546
    What if they were all like Chester, and not the dog.
  • Chester
    Chester Member Posts: 83
    If more customers were like me you guys would be happy because a well-educated consumer is likely willing (should definitely be willing) to pay more for a higher quality installation :-)

    I'm glad I was able to learn that quality of the install is probably more important than brand of equipment. Even then I had no idea what really goes into it until my contractor was on site and I saw the craftsmanship.
    GordyCanuckernjtommySWEI
  • Canucker
    Canucker Member Posts: 722
    Well said @Chester That's why I'm here, just a homeowner trying to learn. As a plus, its helped me at work.
    You can have it good, fast or cheap. Pick two
  • vr608
    vr608 Member Posts: 144
    edited November 2015
    Honestly, @Chester is representative of a lot of us homeowners on here, trying to learn as much as possible and appreciating a trade that isn't nearly recognized as much as it should be due to the very visible "bad apples" that most people are used to complaining about.

    Knowledge is power, but as I've said before, sometimes it sucks having "inside info" and then having so called professionals dismiss what you know because you're an idiot customer that doesn't really know what he wants (I see that a lot in my own line of work, IT). Fortunately Dan runs a great site here that allows a great exchange of information in BOTH directions, homeowners to pros and vice versa.
    Peerless 63-03, 118,000 BTU (308 sqft), single-pipe steam system connected to 286 EDR of radiation, 30ft of baseboard and indirect DHW
    3PSI gauge
  • Paul48
    Paul48 Member Posts: 4,469
    I've spent my whole life learning to do things I couldn't afford to pay someone else to do wrong.
    SWEIjonny88Canucker