Want suggestions for best practices piping to potable expansion tank
Bob Vennerbeck
Member Posts: 107
I've got an Amtrol potable expansion tank installed circa 2001, when we had the lead service replaced and required back flow preventers installed. I suspect the potable tank has failed internally - it's suspended from threaded tee in 3/4" sweated copper running across ceiling as cold supply to water heater, and it sounds 'full' when I thump it. The water heater TPRV has burped and reseated a couple times - so something's clearly amiss. I plan to check my city water pressure with a gauge, shut down water heater, shut off incoming water supply, drop and drain the potable tank, check and recharge to same as city water pressure? slightly higher? - then reinstall if I don't hear hissing through a blown diaphragm, and replace if I suspect a problem. I know it's a heavy wet mess to take down an expansion tank, and I'm thinking of adding isolation valve between tank and cold water supply - then wondered if one valve is enough, or if I want one to leave on the water line, and another on the tank, and maybe a third on a bleeder tee.... am I overthinking this, or do any of you have an favored clever arrangement that makes servicing potable expansion tanks less of a dripping pouring nuisance?
Yes tank pressure same as water pressure.
Use this valve at the exp tank
http://www.supplyhouse.com/Webstone-41672-1-2-Pro-Pal-Full-Port-Brass-Ball-Valve-w-Hi-Flow-Hose-Drain-600-WOGThere was an error rendering this rich post.
Hatteras guy: yes, but at least one valve would be a d...n sight better that what I've got now, and once I start shopping.....
STEVEusaPA: thanks for the link - looks great for hydronics with make-up inlet right at point of no pressure change, but clearly states not for potable use.
So I'm going to swap out my waterlogged-bladder-busted Amtrol ST-12 for a new one, and install a ball valve between the new tank and the existing tee for the NEXT time - and hope that's all that's making the water heater burp. Pretty sure the ST-12 wasn't pumped up to match Providence Water Supply Board delivery pressure when I installed it, because I wasn't that smart fourteen years ago, and where were you guys when I needed you then?0 -
If you depress the Schrader valve and get more than a touch of water out of it, then a new one is in your future. If when the system is drained and after you remove the tank and it weight about 20 pounds, it is done also.0
