black pipe vs copper for condensing combi piping
joca
Member Posts: 27
in Gas Heating
is it ok to use black pipe and fittings for the near boiler piping on mod/con boilers? I know its a closed system, but there is always some rust and sediment,right? The plate heat exchanger seems easily clogged ,as well as TRV's, and mixing valves throughout the system . Should I be concerned?
0
Comments
-
-
Dirtmag would be recommended though0
-
Fernox TF1 Magnetized. Pretty neat. Can install on a bypass.0
-
thanks SWEI, it will be cleaned and maintained,and we have great water here, so i should be ok.
Jonny88, is a dirtmag necessary if i go with copper? The only Fe would be from the panel radiators and the circulators. Is a wye strainer enough protection then? Just want to do the right job-overkill is unfortunately not in the budget.0 -
Dirt mag or TF1 filter are not that expensive and cleaning and adding inhibitor is a snap with either . Cannot say that for the wye strainer , when comparing it is a terrible way to remove nasties . Cleanout of the other 2 is also very clean and easy .You didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38331 -
It is Fernox .You didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38330 -
-
so ,a dirtmag is a good idea in any system is what i'm getting?
perhaps copper is best practice, i can't see any cons with copper-maybe some cons with steel. My preference is copper, but i have steel speed headers (that i 'm thinking of not using now) . I'm also going to switch out a Cast iron air scoop for a spirovent type -i didn't like the 18" lead pipe requirement anyway0 -
It must be regional. Dirtmags in residential aren't seen or even stocked in my part of CT. IMO, don't over think it. There's going to be some ferrous somewhere in the system. The water will become "dead" in short time.0
-
is there a dirtmag that would double as an effective air eliminator?
will have to rework the budget- can't tap into the beer budget!0 -
I never understood why anyone would want to create unneeded turbulence and flow friction using threaded nipples and fittings on a modern system??
Its not a quicker install and then there are those potential leaks then and later down the road.
Also to me a rusting black nipple does not look nice0 -
-
@joca . Look at the Caleffi Sep4 . Hydraulic separator , air eliminator , magnetic dirt separator all in one nice little package / component .
http://www.caleffi.com/usa/en-us/catalogue/sep4tm-4-1-hydraulic-separators-549506aYou didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38330 -
thanks rich , it is nice ,a little pricey,but it does combine components and should save some space . i'll have to read up on it some more to see if it works for my system, and if its worth the redesign. This is how this discussion started- i was compelled to question the original design i was given...0
-
If it's a combi, usually the mfr sells flush manifolds for the domestic and the heating sides, I know navien does. I get them for every job.0
-
Magnets not needed if there is no iron in the system. Note that even panel rads will shed a fair bit of magnetite IME.0
-
So is the Fe in the steel panel rads enough to warrant the use of a dirt mag type component?0
-
No premade manifolds for this unit, doesn't have an integral primary pump0
-
Dirtmag with air eliminator.Not what I ordered as I have a spirovent.Really wanted Sep4 but unavailable .2
-
We frequently find a bit of screwed pipe to be the best option for a portion of the near-boiler piping. If the entire rest of the system is nonferrous (don't forget unlined expansion tanks, BTW) we use Class 150 304 SS. It's less expensive than brass, the fittings are far less restrictive than either brass or iron, and it looks fantastic.HDE said:I never understood why anyone would want to create unneeded turbulence and flow friction using threaded nipples and fittings on a modern system??
Its not a quicker install and then there are those potential leaks then and later down the road.0 -
I see you have both spirovent and discal. If using only the discal , where would you pipe in expansion tank and auto fill .0
-
Always in relation to the pump - the inlet side of the pump.Steve Minnich0
-
I was asking because, isn't there a reason why the expansion tank and air eliminator are combined at the point of no pressure change. Not sure if I'm remembering correctly . I"ll reread "Pumping away" later...0
-
The DiscalDirtMag that Jonny 88 shows is a great way to get air, dirt and ant magnetic particles which may cause issues with ECM circulator if you ever add one.
The expansion tank does not need to be at the air eliminator,but connected at the suction if the circ pump.
With some mod con. Boilers the pump is on the boiler return, so the tank connection should've there.
Air elimination should be at the hottest point in the system,boiler outlet
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Thanks, it's coming back to me , so,air elimination at high temp and low pressure,and expansion at low pressure( off an inline tee in the primary loop would be ok?)0
-
I think Hot Rod would agree? If a mod-con is piped P/S and the majority of them are, I like to put the air separator on the supply side of the system loop just ahead of the system circ., not the boiler loop.Steve Minnich0
-
when you say "system loop," is that the primary loop,with the boiler loop and the zones being secondary loops or are you considering the boiler loop(with internal circulator) the primary?0
-
Most terminology dictates that the primary loop is the boiler loop and that the secondary loop is the system loop.
Steve Minnich0 -
Not to confuse the issue but some, myself included, prefer to think of the secondary loop as the one being fed by the closely spaced tees which is often the boiler loop in a mod-con application.Steve Minnich0
-
that was my confusion, i consider the secondary loops the ones being fed by the closely spaced tee also. i was planning to have the primary loop pass thru the boiler-its a single zone system so i'm trying to understand how to streamline things a bit. i know i'm getting off topic, but it seems odd to do a P/S with 2 circulators to feed a single zone?0
-
Secondary loops are off the tees, yes. Many of the boilers and solar thermal systems we work on are by that definition secondary. Bristol Stickney showed us how to build a primary loop there which does not need a circulator.0
-
-
thanks, makes sense. I'll have to research stickney's piping (it's beyond my needs right now, but you got me curious)0
-
Just be aware with Bristols P/S, the one with check valves between the take offs, you keep putting the various pumps in and out of series as they start and stop.SWEI said:Secondary loops are off the tees, yes. Many of the boilers and solar thermal systems we work on are by that definition secondary. Bristol Stickney showed us how to build a primary loop there which does not need a circulator.
It is a clever approach, just know the flow conditions you are modifying.
In Bristols August column in PHC News he shows a P/S with a primary pump. I have seen him draw it both ways.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements