Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Peerless oil boiler temperature gauge reading low

Options
Noluck
Noluck Member Posts: 12
I have a Peerless oil boiler the aquastat is set at
Low 170 Hi 190
But the Guage on boiler is only reading 125
PSI IS 18

It has a tankless coil I have the hot water running in the shower and the boiler kicks on and runs but shuts down when gauge reads 125

Comments

  • Noluck
    Noluck Member Posts: 12
    Options
    Yes it is scalding
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    edited October 2015
    Options
    Your gauge doesn't work. To confirm, take a food thermometer, put it in a small pot of water in the sink. Run the hot water into the pot.
    Why is the low limit set to 170?
    You should also have a mixing valve to prevent scalding

    There was an error rendering this rich post.

    billtwocase
  • j a_2
    j a_2 Member Posts: 1,801
    Options
    Maybe it doesn't work, That's a good guess.....there is a heat compound that is good to use in the wells of the probes...One quick question, what type of system is it high mass or low mass? Is there a boiler bypass installed? Asking because as always a pic should be posted so we can tell what kind if install we are dealing with.?
  • Patchogue Phil_2
    Patchogue Phil_2 Member Posts: 304
    Options
    Oh how I hate a cliffhanger .....

    :#
  • j a_2
    j a_2 Member Posts: 1,801
    Options
    Hay they all come back...when they need us....