HW baseboard Ghost Flow

Options
Patchogue Phil_2
Patchogue Phil_2 Member Posts: 304
edited October 2015 in THE MAIN WALL
Mom's house was 76 today with tstat down to 60. Baseboards very warm. I'm figuring it's ghost flow, heat rises etc.

Not sure if there is any check valve, but see attached pic (having attachment issues). Looks like there is a lever on top. What does it do?

I don't recall the house experiencing such hot ghost flow before.

Comments

  • hot_rod
    hot_rod Member Posts: 22,139
    Options
    Did it just start this season? Any changes made to the system?
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Patchogue Phil_2
    Patchogue Phil_2 Member Posts: 304
    Options
    No changes that I know about. And i dont think this was a problem last year but maybe my mother didn't notice. Or she chose not to complain. Coulda been ghost flowing all Summer too, with a/c running.

    Might been after hurricane Sandy or noreaster, house had no power for 11 days. But Thermopile keeps burner running. Maybe someone opened the valve to bypass?

    So from the pic, is the flow check bypassed? How can I determine if functioning correctly to stop ghost flow?
  • Patchogue Phil_2
    Patchogue Phil_2 Member Posts: 304
    Options
    Lever is currently "pointing" perpendicular to pipe. If it is pointing "North", flow arrow on valve body is pointing West from East.

    I'm looking for internal diagram. Anyone know how the function physically and how they could fail?