mod-con with high temperature emitters

Options
hot_rod
hot_rod Member Posts: 22,139
edited October 2015 in THE MAIN WALL
At last weeks Coffee with Caleffi webinar, Jody did a fine job of showing and explaining the concept.
Using ASHRAE Hours of Occurrence data you can determine what % of the season you are at, below or above design condition. This example was for Boston.

With this data and a proper ODR installed and adjusted you may be able to allow the boiler to run in condensing mode for much of the season.

The 1 hour webinar is archived at this link, webinar #10

https://www.youtube.com/watch?v=6mNECDHgDrg&list=PLuuV0ELkYb5VE0I4evUZ30b5U78CRlRdg&index=10

Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream
Tinmankcopp

Comments

  • NYplumber
    NYplumber Member Posts: 503
    Options
    HR, the webinar was nicely organized. A good watch even for those that are fluent in combustion and modcons. You never know where you can pick up a tip or two.
    :NYplumber:
  • Henry
    Henry Member Posts: 998
    Options
    Of the 1050 heating hours here, only 150 hours are at maximum boiler design temperature.