mod-con with high temperature emitters

hot_rod
Member Posts: 25,124
At last weeks Coffee with Caleffi webinar, Jody did a fine job of showing and explaining the concept.
Using ASHRAE Hours of Occurrence data you can determine what % of the season you are at, below or above design condition. This example was for Boston.
With this data and a proper ODR installed and adjusted you may be able to allow the boiler to run in condensing mode for much of the season.
The 1 hour webinar is archived at this link, webinar #10
https://www.youtube.com/watch?v=6mNECDHgDrg&list=PLuuV0ELkYb5VE0I4evUZ30b5U78CRlRdg&index=10
Using ASHRAE Hours of Occurrence data you can determine what % of the season you are at, below or above design condition. This example was for Boston.
With this data and a proper ODR installed and adjusted you may be able to allow the boiler to run in condensing mode for much of the season.
The 1 hour webinar is archived at this link, webinar #10

Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream
trainer for Caleffi NA
Living the hydronic dream
2
Comments
-
HR, the webinar was nicely organized. A good watch even for those that are fluent in combustion and modcons. You never know where you can pick up a tip or two.:NYplumber:0
-
Of the 1050 heating hours here, only 150 hours are at maximum boiler design temperature.0
Categories
- All Categories
- 86.9K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 425 Carbon Monoxide Awareness
- 109 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 105 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 975 Plumbing
- 6.3K Radiant Heating
- 387 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements