Sizing a steam boiler
Options
fab4ever77
Member Posts: 8
Looking at Burnham IN line, 1200 sq ft. home, EDR total is 391.
Which Burnham IN would you recommend?
IN4=65,000 BTU output
IN5=86,000
IN6=108,000
I'm guessing the IN5 is the best one for me, but what would happen if I buy the IN4 instead?
Thanks!
Which Burnham IN would you recommend?
IN4=65,000 BTU output
IN5=86,000
IN6=108,000
I'm guessing the IN5 is the best one for me, but what would happen if I buy the IN4 instead?
Thanks!
0
Comments
-
The IN4 is rated at 271 sq. ft. EDR. that is way too small and leaves you no pick-up/piping factor. The IN5 is rated at 358 sq. ft and would leave you about 20% pick-up factor. The IN6 is way too large @ 450 sq.ft, about 15% over-sized plus the 33% pick-up factor. You will likely get a lot of short cycling with the IN6.
The IN5 is the best pick in the Burnham IN line.0 -
-
Sure about the EDR. 8 radiators and some are oversized in our old home0
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements